After installing my generator transfer switch panel I got curious about the ratings on residential main panels. I assume when one is rated for 200 amps, say, that the limiting factor is the size of the bus bars? Likewise the largest main breaker that you can install in such a panel is 200 amps.
But is there a limit in code as to the total circuits and loads that can be connected? I have a 200 amp panel with 17 15 amp 120v circuits, 2 20 amp 120V circuits, 2 30 amp 240v circuits and one 15 amp 240v circuit. That is way more than 200 amps (I realize that you will never have anything close to full load on all circuits without really trying). And the panel has a lot of space for even more breakers. Just curious if there is a NEC limit or guideline for how much load can be installed in a panel as compared to the full panel rating... or can you just install as many circuits as you have room for breakers in the panel?
Live long and prosper.
raylo32 is online now   Reply With Quote
The Following User Says Thank You to raylo32 For This Useful Post:
wlibolt (08-09-2015)
Old 08-21-2012, 02:04 PM   #2
Master Electrician
If its anything like our code there's a maximum amount of breakers you can install for service size. There's also a set of guidelines to do load calculations that will determine the service size itself.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 08-21-2012, 02:25 PM   #3
joed's Avatar
Rewards Points: 12,852
There used to be a 42 breaker maximum per panel but I think that was lifted in the last NEC code cycle. It depends on what code version your region is using.
Old 08-21-2012, 02:44 PM   #4
raylo32's Avatar
AFAIK our state and county just cites the NEC. I didn't count the total spaces in my panel but I think there are ~40 or so.... not that I need any more circuits than I already have connected.
Old 08-21-2012, 03:28 PM   #5
kevinp22's Avatar
I just had an electrician install a new 200A service and panel in my house. I wanted to stay with Cutler Hammer CH and 42 space was the largest panel available.
kevinp22 is offline   Reply With Quote
Old 08-21-2012, 03:35 PM   #6
Master Electrician
Rewards Points: 3,864
The total connected load is what is important, not the total amperages of the individual circuit breakers.
brric is offline   Reply With Quote
The Following 2 Users Say Thank You to brric For This Useful Post:
Jim Port (08-22-2012), kevinp22 (08-21-2012)
Old 08-22-2012, 07:17 AM   #7
joed's Avatar
I Canada we can get 40/80 slot panels at home depot.
Pex: home-run vs Brach? Why not both? teeman11 Plumbing 7 03-15-2012 09:43 AM
Limit to how many circuits can be in a panel? adpanko Electrical 11 02-15-2012 10:20 AM
Multiple circuits losing power Skip72 Electrical 6 09-20-2010 10:27 AM
Thoughts on wiring new attached garage/hallway Mi Feller Electrical 45 06-18-2010 06:47 PM
Adding odd circuits in a bedroom and hood fan oh my! beatle Electrical 3 11-19-2009 07:45 AM