Starting a DIY 200 amp service entrance. By code is #6 copper wire excepted from meter to 8ft ground rods? Unsure if #4 wire is required with 200 amps. thanks for any help.
redleg23 is offline   Reply With Quote
Old 08-20-2011, 09:33 AM   #2
Code05's Avatar
Rewards Points: 1,104
Grounds rods never need larger than a #6. If you have a water pipe or other electrode connection the rules are different.
Code05 is offline   Reply With Quote
Old 08-20-2011, 09:34 AM   #3
Nope, no water lines involved. thanks
Old 08-20-2011, 09:35 AM   #4
Rewards Points: 1,548
200 amp. service requires #3 copper wire from panel to water pipe that qualifies as a ground electrode however you can use #6 to ground rods.
Old 08-20-2011, 09:42 AM   #5
Code05's Avatar
#3? T250.66 says #4 Cu or #2 Al.
Old 08-20-2011, 10:04 AM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,990
Also, the grounding electrode conductor in most areas should NOT originate from the meter pan. It should originate from the main panel/disconnect.
Most POCO's have eliminated the option of placing the GEC connection from inside the locked meter pan.