Old 10-10-2012, 02:51 PM   #1
200 amp panel
Have an existing 100 amp panel connected underground to a private pole and then overhead to Hydro. Building a garage between the private pole and Hydro and installing a 200 amp panel with a underground wire to the existing power supply at the private pole. How do I wire the panel for the lead to the existing power supply?
Chris Bl is offline   Reply With Quote
Old 10-10-2012, 03:36 PM   #2
joed's Avatar
200 amp panel
New panel will need the neutral and ground bonded with ground rods. The feed to your existing panel will need four wires as the ground and neutral need to be separated in the old panel.
Install a 100 breaker in you new panel to feed the old one.
Do not PM with questions that can be asked in a forum. I will not respond.
Old 10-10-2012, 03:54 PM   #3
200 amp panel
Without knowing the distances involved and the current wire size, we can't say anything for certain. But, the wire between the pole and the house maybe undersized based on the total run. So, you may need to replace the wire between the existing pole and the house (either on sizing or for another conductor). In that case, it might be better to do a direct run from the new panel to the existing panel.
Have you talked to Hydro about your plans? Some power companies do not allow a new structure to go in under their drop, and will insist on moving it to,or near, the new structure. Even if they allow it, they will have a minimum clearance required between the overhead wire and the roof.
Oso954 is online now   Reply With Quote
Old 10-10-2012, 04:44 PM   #4
Contractor
Dan101's Avatar
200 amp panel
I agree with oso. You Should contact Hydro first because it will save you lots of problems.
Dan101
Owner
J.& D. Remodeling
Chicago, IL
Dan101 is offline   Reply With Quote
Sub panel to sub panel feeding tvfd27 Electrical 1 08-21-2012 04:01 PM
Section 310.15(B)(6) vs. 210.4. Don't assume, call your friendly AHJs! Daneel Electrical 3 04-11-2012 08:24 AM
Sub Panel SoxFan Electrical 2 12-02-2008 11:16 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 04:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM