Old 11-26-2012, 10:07 PM   #16
Rewards Points: 152
Originally Posted by brric View Post
That panel needs a hub or sealing washer. Is the lower end of the emt with the ground wire bonded on the lower end?
Ok, easy fix on the #4 ground wire. I'll put in PVC and do away with EMT.
Now the other. AEP won't allow a bonding bushing in their can. I will put it in my panel. However, do I need to put a hub on the bottom of the offset and a ground bushing below the hub inside my panel? If so, it has to be Myers type with the grounding bushing screwed on.
Instead, a sealing washer topped off with a grounding bushing seems to be an easier installation. Does the bonding jumper need to be #4?
I flat out forgot about the sealing washer. Duh but I've never seen our local sparkies use grounding bushings. Maybe the local AHJ likes what he sees in 250.92(B)(2) and calls it a day.
n175h is offline   Reply With Quote
Old 11-26-2012, 10:18 PM   #17
Rewards Points: 152
[quote=n175h;1061337]Does the bonding jumper need to be #4?
I think I found it. Looks like Table 250.66 says it has to be #4. Am I reading it correctly?
Old 11-27-2012, 10:46 AM   #18
Rewards Points: 152
Down to the electric supply I went and picked up sealing washers and grounding bushing. I installed the sealing washer/locknut under the hub and the grounding bushing threaded on next. Ran #4 wire to the ground bar.
One concern I have is the rain hub on top of the meter can came with no bushing of any type. Do I need to bush below the hub at the can penetration? You can see there is nothing there in the 1st picture. Everything else I think I covered.
I replaced the emt with non metalic liquid tite flex conduit. PVC would not land in the knockout hole in the meter can and pass behind the main disconnect. No room.
200 amp meter loop critique my work-meter-loop-revised-001.jpg   200 amp meter loop critique my work-meter-loop-revised-002.jpg   200 amp meter loop critique my work-meter-loop-revised-003.jpg
Old 11-27-2012, 04:50 PM   #19
Rewards Points: 152
I found a plastic knockout bushing that snapped into the bottom of the rain hub at the electric supply house. That should wrap this project up. I believe I'll call the inspector and hopefully I'll pass and get AEP to drop me some power. It takes about 6 weeks to get power out here in south TX because of the oil boom we are experiencing.
Old 12-06-2012, 09:01 PM   #20
Rewards Points: 152
I passed
Ordered a service contract and AEP came out and hooked it up in 4 days. Wow! Wasn't expecting that. Now I can start building my shop. I'll continue to post pictures if anyone is interested. Got to start burying pipe pretty soon.
Old 12-06-2012, 09:29 PM   #21
Electrical Contractor
jbfan's Avatar
Rewards Points: 548
Great job!
Old 01-31-2013, 06:19 PM   #22
Rewards Points: 152
Moving on to the inside of the building now. I've been erecting the building for over a month, but had a chance to land my sub panel. I ran 1/0 THWN wire for 150 amps. Couldn't find a breaker locally, so I stabbed a 125 in for now that I had in the storeroom. I ran #6 ground back to the main and landed a #6 bare ground wire bonded to the metal building frame and clamped to a #4 20' rebar as my CEE. The #6 wire is continuous with no spices for ground bar to CEE. Neutral is isolated from ground.
Anyone see any errors? I have to get this inspected after I finish all the wiring.
I've got to clamp those pipes since it is 3' 2" between supports. Should have moved the box lower.
Also, I ran that #6 wire through a romex clamp to exit the box. That OK??
200 amp meter loop critique my work-logs-009.jpg   200 amp meter loop critique my work-logs-010.jpg   200 amp meter loop critique my work-logs-011.jpg   200 amp meter loop critique my work-logs-014.jpg
Old 02-01-2013, 11:18 AM   #23
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
I have used a romex clamp many times when they did not have a small hole for the ground wire to fit though.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 02-15-2013, 04:58 PM   #24
Rewards Points: 152
I'm almost finished. Still need my light fixtures, but I'm done pulling home runs. Here is my panel. How's it look? Orange for the 240's, red for the lights, black for the 120's. #6 wire pair for welder, and one set for the RV. I ran grounds with each pipe run and put bond jumpers in each j-box.
I ran several multiwire branch circuits which caused me to land two GFI plugs in one box in order to send out the separate circuits downstream to the daisy chain in each direction down the wall. It's okay, but I don't really like it, but code says you gotta have em.
I ganged a couple of 240's with some 120's for convenience and a table saw, etc. I like that setup.
Should be ready for final inspection next week after I hang the T8 fixtures.
200 amp meter loop critique my work-panel-finished-001.jpg   200 amp meter loop critique my work-panel-finished-002.jpg   200 amp meter loop critique my work-panel-finished-003.jpg
Old 02-15-2013, 05:55 PM   #25
rrolleston's Avatar
Looking good.
Can homeowner (or friend) rewire in California? cvandewater Electrical 34 01-14-2012 12:04 PM
Insulated metal grounding bushing in meter socket WillK Electrical 7 05-26-2011 09:10 AM
short circuit. reset the breaker, but no power bp91708 Electrical 10 03-18-2011 10:07 AM
How does electricity meter calculate kwh? deerhunter Off Topic 18 09-06-2010 08:26 AM
Duct work in garage. flashme18 HVAC 1 11-08-2009 06:29 PM