Originally Posted by rrolleston View Post
Since you have a disconnect outside you need a four wire feed and your neutral and ground need to be separate.
Besides it being a code issue, why do the commons and neutrals need to be seperated? What would that do electrically? The reason I ask is the panel I removed had all grounds shoved into one bar, and it worked just fine. It crossed my mind to seperate them but I didn't purchase any additional bars and the nearest store is 70 miles from here. And if required to seperate them why would there only be 40 ground screws in a 40 circuit panel, shouldn't there be 80...? Just curious...
Kodyb is offline   Reply With Quote
Old 01-15-2013, 09:52 PM   #17
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
The grounding conductor is not allowed to carry current. If you were to lose a neutral connection the metal of the panel could end up energized. With a ground and a floating neutral that would be isolated if it happens. With your panel you could add a ground bar to both sides of the panel and just move your grounds off to the sides onto the ground bar. And connect the two ground bars with some ground wire.
You would also have to remove your bonding screw from the panel.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 01-15-2013, 10:10 PM   #18
Okay, not that I'm doubting you, I just want to understand... Then why do some panels (a few square d panels I looked at) literally had the common and neutral lugs on the same unbondable buss right next to each other?
Old 01-15-2013, 10:24 PM   #19
rrolleston's Avatar
Some have them both on there and they have a screw you set in or a wire that connects to the metal of the panel and then to the bar. And some panels are not made usable as sub panels without adding the proper grounding or neutral bars.
Old 01-16-2013, 12:14 AM   #20
Thank you for the clairification...
The first chance I get - I will purchase additional bars and get them installed and seperate the grounds, thanks again...
Old 01-16-2013, 12:27 AM   #21
rrolleston's Avatar
For 200 amp you just need #4 al for a ground and make sure you have two ground rods and a water main ground
Old 01-16-2013, 08:45 AM   #22
eastcoastsparky's Avatar
Rewards Points: 150
You dont know if the sub panel is in same house or detatched
Sent from my iPhone using DIY Forum
eastcoastsparky is offline   Reply With Quote
Old 01-16-2013, 08:48 AM   #23
Old 01-16-2013, 08:50 AM   #24
Thanks!! I appreciate the constructive input...
Heat for a basement with Pellt Stove on Main Floor magnum44 HVAC 1 11-20-2011 08:55 AM
Main Electric Panel Help Redrum Ninja Electrical 13 10-22-2011 07:28 PM
Adding ground bar to main panel WoodworkerDave Electrical 6 09-27-2008 04:52 PM
Replace main panel? And lots of other ?s Bcoleman6 Electrical 13 01-22-2008 09:40 AM
main lug vs main breaker for sub panel diyll Electrical 1 01-17-2008 08:18 PM