200 amp main panel
How many breakers can I put in a 200 amp main panel? I have 2- 100 amp sub panels running off main also. They are using a 30 amp 2 pole breaker for each. Just wanna make sure I don't overload my panel.
Sent from DJ's iPhone
Djennis20 is offline   Reply With Quote
Old 09-30-2011, 08:39 AM   #2
I=E/R
a7ecorsair's Avatar
As many as it will hold. Breakers don't establish the load.
a7ecorsair is offline   Reply With Quote
Old 09-30-2011, 08:51 AM   #3
So I can load my panel to the gills with 20 and 30 amp breakers without worry?
Old 09-30-2011, 08:51 AM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,274
If the breakers in the main panel are 30 amp, you do not have 2 100 amp sub panels, you have 2 30 amp sub panels. If the subs have 100 amp main breakers they are merely disconnects.
+1 on as many breakers as you have slots for. You need to do a load calculation to determine if you are approaching the 200 amp capacity.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 09-30-2011, 09:39 AM   #5
I=E/R
a7ecorsair's Avatar
Your main breaker will limit the total current.
Old 09-30-2011, 11:40 AM   #6
So, in a 200amp main panel, the breakers(amps) can only add up to 200 total?
Old 09-30-2011, 11:41 AM   #7
Or is it 200amps on each side?
Old 09-30-2011, 12:34 PM   #8
A "Handy Husband"
rjniles's Avatar
The total load cannot exceed 200 amps, the number of installed breakers is meaningless. The total of the installed breakers in my 200 amp panel is 425 amps. Doesn't mean a thing.
Old 09-30-2011, 12:44 PM   #9
I=E/R
a7ecorsair's Avatar
Branch circuit breakers are for protecting the wire of a specific circuit. The amperage of the breaker has nothing to do with panel amps. If you have a 200 amp panel then your main breaker will have 200 on the handle. Your main breaker may look like two breakers with 200 on each breaker and a tie bar.
That is 200 amps at 240 volts.
Old 09-30-2011, 12:59 PM   #10
Ahhh, gotcha. Thanks for the info.
Old 09-30-2011, 02:15 PM   #11
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
I am not sure where I see that anybody wrote that.
On the contrary, they are <correctly> telling you that the sum of the breakers means absolutely NOTHING.
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 07:15 PM