Old 01-30-2009, 12:57 AM   #1
200 amp feed thru panel
What is the difference between a standard 200 amp panel and a 200 amp feed thru panel.
leroy is offline   Reply With Quote
Old 01-30-2009, 01:16 AM   #2
DIYer
It has a second set of lugs so that you can tap the mains to a second panel. If you do this with service conductors, you need to be able to reach all the main breakers without walking, so the other panel has to be right next to it generally.
Gigs is offline   Reply With Quote
Old 01-30-2009, 06:53 AM   #3
Electrical Contractor
wirenut1110's Avatar
Send a message via AIM to wirenut1110
If you're talking about main breaker panels with feed through lugs, it's mostly used as a disconnect to feed a 200 amp main lug panel and only has spaces for 8 branch breakers. It's usually a 3R enclosure but I'm sure it's available in indoor.
I use them on service upgrades where a heat pump is being installed and a service disconnect is required.
Use the feed through to a new main lug panel in the house with exisiting circuits, and feed the new loads from the feed through panel.
This isn't true. When you use the feed through lugs, the panel you're feeding is a sub-panel so if you cut the main breaker off it will kill your sub too.
wirenut1110 is offline   Reply With Quote
Old 01-30-2009, 07:00 AM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
HUH???
Can you explain this a bit better?
I know this is not a requirement, so I am wondering where it is you heard of this.
A feed-thru panel has lugs right off the main buss so the full amperage of the panel can be fed on to another panel. This eliminates the need for a feeder breaker that would be limited to typically 100 or 125A.
Say your main drop or underground came into your detached garage. Then on to the house. You could have a feed-thru panel in the garage that will have 6-8 circuits, and also allow the full 200A to continue on the the house without a sub-feed breaker. The main breaker serves this purpose.
The house, being a detached structure would still require a means of disconnect, so another main breaker panel would likely be used simply for convenience.
Speedy Petey is online now   Reply With Quote
Old 01-30-2009, 01:28 PM   #5
DIYer
I guess we are talking about different things. I'm speaking of small panel with just lugs at the top and bottom. This would be subject to the rule about 6 breakers since it would all be unfused if used with service conductors before a larger panel with a main breaker in it.
Here's a sheet from square D about what they call the various types:
http://ecatalog.squared.com/techlib/...0089268007935e
Old House Rewire finnimus Electrical 15 05-13-2011 11:39 PM
Adding a second Electric sub panel TW Lucas Electrical 9 10-05-2008 03:37 AM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 11:27 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 04:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM