Old 09-25-2012, 06:20 PM   #1
200 amp disconnect breaker from meeter box
I just had service put in a building out back. The main disconnect breaker keeps tripping. All wiring is correct and has passed two electrical inspections.
Question... Can the 200 am breakers be bad, go bad, or come from the factory bad? Oh, and there is 250 at the meeter. I tested it and it does have it at the meeter.
Stuart Hamilton is offline   Reply With Quote
Old 09-25-2012, 06:28 PM   #2
kevinp22's Avatar
yes, breakers can be defective.
when you say 250 at the meter, do you mean amps or volts. Also, do you mean that this service out back has a separate meter or is it a subpanel that branches from your main panel.
Also, is the main at the outbuilding or at the house tripping?
kevinp22 is offline   Reply With Quote
Old 09-25-2012, 06:29 PM   #3
Electrical Contractor
Who did the work?
You need to call them back to check it.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 09-25-2012, 06:29 PM   #4
It is unusual, but not unheard of to have bad breakers out of the box. 250 what at the box?
ionized is offline   Reply With Quote
Separate 110 and 220 receptacles on 2-pole 220 V Square D GFI breaker sunrise Electrical 1 05-13-2012 08:27 PM
Outside breaker, inside main breaker panel, so is it a sub? CPF Electrical 29 02-01-2012 11:28 AM
GFCI Breaker Tripping Spa Light eaposition Electrical 21 09-08-2010 10:57 PM
Breaker problem jdhar Electrical 11 06-10-2009 02:18 AM
Sq D Trillaint Breaker problem jmreynol Electrical 3 04-28-2009 08:06 PM