200 Amp To 100 Amp To 60 Amp - Electrical - DIY Chatroom Home Improvement Forum
Old 11-13-2012, 08:12 PM   #1
200 amp to 100 amp to 60 amp
i need a diagram of nec approved wiring from 200 amp main to a100 amp attached panel to a60 amp detached panel?
ekyme is offline   Reply With Quote
Old 11-13-2012, 08:15 PM   #2
Licensed electrician
Rewards Points: 1,622
The required wiring method would depend on the environment the feeders needed to run through.
All wiring methods would need to be 4 wires unless a metallic conduit was used.
ekyme (11-13-2012)
Old 11-13-2012, 08:24 PM   #3
200 to 100 is in pvc above ground underneath eve from 100 to 60 is below ground 18 inch inpvc
Old 11-13-2012, 08:35 PM   #4
does 4wire need ground bar and ground rod at each panel down stream
Old 11-13-2012, 08:46 PM   #5
Each panel will get a separate ground bar. Only subpanels in a detached structure get a grounding electrode system like rods.
Old 11-13-2012, 08:53 PM   #6
do i bond the ground at the 100 amp attached panel?
Old 11-13-2012, 09:00 PM   #7
You only bond the neutral to ground in a service panel. Not any panel downstream.