2 Unit Help... - Electrical - DIY Chatroom Home Improvement Forum
Old 04-05-2012, 07:20 AM   #1
Question
2 unit help...
I just bought a 2 unit home..but....found there is only one 200 amp meter and electrical panel... I want to keep the main unit (1000sq.ft)downstairs on the 200 amp panel (where I will live), and the second unit upstairs a 100 amp panel since its smaller 700sq.ft.
Do i need a 200 amp double meter? What size service feeder? and disconnects???? HELP!!
landlordhelp is offline   Reply With Quote
Old 04-05-2012, 07:25 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
In many places you can simply add a 100A service right next to the existing one.
Are you doing this or will you hire an electrician? What is your level of expertise?
Old 04-05-2012, 07:31 AM   #3
I've done electrical work in the past and can change service.... the electic company says the meter has to be moved to the other side of the house so i will put the disconnects there and the existing pane will stay where it is and the 100amp panel will be installed in the upstairs apartment..
Will i need a 2 meter 200 amp meterbase & 200 amp disconnects or can i wire a 100 amp disconnect off one side of the meter with 100amp service cable... is that allowed by code?
Old 04-05-2012, 07:32 AM   #4
Old 04-05-2012, 08:27 AM   #5
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Depending on the existing wiring, this may not be even possible without a major rewire of the house. I would bet that, if the house has always had one service, that the circuits are intermixed between the first floor and second floor.
I would check with the local electrical inspector as he MAY require a third panel for the "public" areas.
Old 04-05-2012, 08:38 AM   #6
Ill be living in the bigger apartment so a common area panel isn't an issue... and i already started seperating the circuits, it was easy since each apartment was wired seperately even though they all went to the same panel... I'm adding junction boxes were needed and have attic access to run new homeruns to the upstairs unit..
Old 04-05-2012, 08:58 AM   #7
k_buz's Avatar
Keep in mind that when you are running new home runs, the circuits you connect them to will need to follow the current code cycle for your area.
For example: If you need to refeed a kitchen circuit, it will need to be a 20 A circuit, and the outlet you are refeeding will need to be a GFI. If you are refeeding a general lighting/outlet circuit, it will need to be put on a AFCI breaker.
Old 04-05-2012, 09:02 AM   #8
It's actually wired correctly... the only new additional work is, remove all electric baseboard heaters and wires, add 2 central hvac units, wire the garage and 2 seperate laundry rooms.
Old 04-05-2012, 09:13 AM   #9
k_buz's Avatar
I was just going off this statement...
But it seems as if you got it under control.
Old 04-05-2012, 09:34 AM   #10
k_buz's Avatar
Typically, we would install a 150 A service with 2 100 Amp panels.
You might be able to install a 2/G (duplex) meter/main combo with 100 A mains and reuse the 200 A panel, but I would check with the electrical inspector before assuming anything.
If you install 100 A mains, you would need to run #3 CU or #2 4-wire SER cable between the mains and sub panels. The line side of the meters would decide on what size the service coming to the house is rated at. I have learned thru these forums, there are a multitude of different local and POCO requirements to tell you for sure what are normal sizes for your area. This is why I recommend discussing the service change with the AHJ.
Shoot, we don't even know if you can legally do the work in your area.
Tags
200amp , meter , muli unit , panel , service
Ruud Pack unit "KABOOMS" upon First Light Up of the Day! Wirenut2tite HVAC 18 12-15-2012 11:11 AM
Had an Aire-Flo AC installed, looking for opinions mikemcd HVAC 14 08-01-2011 05:07 AM
Old carrier unit trouble hdbg62 HVAC 18 06-29-2011 09:57 PM
new r-410a ac unit installation procedure(w/old unit r-22)? excalibur1 HVAC 0 06-06-2011 04:47 PM
Window A/C Unit and Supplying Power JayEnder Electrical 1 04-30-2011 08:50 PM