2 Switches, Working On Same Circuit HELP!! - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-22-2013, 10:52 AM   #16
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 5,426
Originally Posted by MTN REMODEL LLC View Post
Jim... I agree that we should all have grounded circuits... but as curiosity because of my ignorence... how does code address extending an ungrounded circut.,,, or does it just say we shoulod not extend one.
Would a GFI suffice with a "no Eqip ground" label as applicable... or what about a ceiling light.
Edit: Answers from me not necessarily based on the National Electrical Code ( local amendments and my guess may apply)
Originally Posted by Jim Port View Post
That section only applies if two prong receptacles were being replaced. It does not apply to other applications like extending an ungrounded circuit.
Jim.... I guess the question would be: Does code prohibit extending an ungrounded circut either (or both) to a receptical or to a lighting fixture.?
(No one is saying it's good....although it was satisfactory prior to the 60's?)
MTN REMODEL LLC is offline   Reply With Quote
Old 05-22-2013, 10:53 AM   #17
Licensed electrician
Rewards Points: 1,028
We cross posted. Look at my response above yours.
MTN REMODEL LLC (05-22-2013)
Old 05-22-2013, 11:00 AM   #18
Rewards Points: 2,512
see if this is better
hammerlane is offline   Reply With Quote
Old 05-22-2013, 11:09 AM   #19
Hammerline..... Don't mean to go off thread.... but how do you guys drawthis stuff.... or where can I go to find out. Is this site software or soe kind of drawing s/w you have.
Old 05-22-2013, 11:18 AM   #20
I use microsoft paint program, Turn the canvas light gray and get to drawing using the line tool. For the devices I just save piictures and paste them in.
Old 05-22-2013, 11:26 AM   #21
Thank Ya Sir....... (For some reason I don't have my "Thanks" button on the screen)
Old 05-22-2013, 11:41 AM   #22
Heres the template I start with. Has many of the common devices on it already.
The Following User Says Thank You to hammerlane For This Useful Post:
Old 05-22-2013, 01:51 PM   #23
Rewards Points: 506
Sorry for the delay. Here is 250.130 regarding ungrounded extensions.
(C) Nongrounding Receptacle Replacement or Branch
Circuit Extensions.
The equipment grounding conductor
of a grounding-type receptacle or a branch-circuit extension
shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system
as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure
where the branch circuit for the receptacle or
branch circuit originates
(4) For grounded systems, the grounded service conductor
within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar
The new wiring needs to be grounded. Often times getting a ground back to one of the acceptable connections is a whole lot of work.
Okay, BUT ...
"The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension"
What about if we extend it with a 2-prong receptacle, which has no ground screw?
Installation is the Reverse of Removal.
Old 05-22-2013, 02:17 PM   #24
New wiring need to meet the current codes, so trying to extend the circuit for another 2 prong receptacle seems kind of counterproductive and does not seem to satify the code IMO.
Old 05-22-2013, 05:11 PM   #25
Rewards Points: 506
Jim??
I think it may satisfy code because of what I quoted, and 250.130 seems to refer only to grounded type receptacles and circuits.
(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding conductor shall not be connected between the grounding-type receptacles.
As to counterproductive, the cost is less than running new circuit, or running an EGC back to the panel, if the existing is ungrounded.
Old 05-22-2013, 05:30 PM   #26
Code does seem to read that way....
Old 05-22-2013, 05:45 PM   #27
Rewards Points: 506
Please explain this to me, as I'm real slow
Old 05-22-2013, 05:49 PM   #28
An ungrounded 3 prong can be downstream of a GFI.
Old 05-22-2013, 06:40 PM   #29
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
The Following 3 Users Say Thank You to stickboy1375 For This Useful Post:
frenchelectrican (05-22-2013), Jim Port (05-22-2013), sirsparksalot (05-23-2013)
Old 05-22-2013, 07:04 PM   #30
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
What you are missing is that the article you are quoting is telling you how you can "pick up" a ground to legally extend an ungrounded circuit. You cannot extend an ungrounded circuit without providing a ground connected to one of those points.
The Following User Says Thank You to k_buz For This Useful Post:
weird wiring and wierd voltages on 3 dual switches... meweber1000 Electrical 5 12-18-2012 01:37 PM
Two sets of 3 way switches on one circuit. Aron063 Electrical 3 09-21-2011 10:24 AM
Light switches not working in bedrooms MasterNES Electrical 27 08-25-2010 12:27 AM
How to wire three switches on one circuit Abs777 Electrical 12 03-25-2010 04:15 PM
Just for fun Andy in ATL Electrical 56 10-20-2009 10:33 AM