1. if i install a subpanel that is fed off of the existing main panel, and i connect the ground of the subpanel to the ground bus on the main panel, does the subpanel still need to be grounded, i.e. connected to a grounding rod outside? i think the answer to this is yes because that is how i was told it needed to be done for my detached shed and i did it like that and everything works fine. however, the one difference here is that both the main and the subpanel are in the same physical building whereas the shed is detached and i was wondering if the grounding requirements may be less strict because of that. if i have to connect it to a new grounding rod, the subpanel option is out the door cause it would be very difficult to set one (very limited patches of dirt between the house and the street).
2. is it possible to put a meter on a subpanel? e.g. if i have tenants living in one of the apartments and they have their own panel with such a meter mounted before the wire goes in, can it be used to gauge their usage vs. the total monthly bill? obviously, the best solution would be to get separate meters but that is hellishly expensive in my area and i cannot afford it right now.
thanks
Old 07-15-2012, 01:11 PM   #2
MarginallyQualified
Rewards Points: 2,464
Originally Posted by amakarevic View Post
...a subpanel that is fed off of the existing main panel, and i connect the ground of the subpanel to the ground bus on the main panel...
the 4 conductors and BONDING to the water pipe should/will be adequate
...possible to put a meter on a subpanel?
sorta... you could use an aftermarket and non PSC approved meter.
You also might be able to put in a meter pack... but this Q is more about zoning issues and whether you can have two SERVICES there but probably not.
Old 07-15-2012, 01:16 PM   #3
Code05's Avatar
Rewards Points: 1,104
A sub panel in the same structure would only require a 4 wire feeder. No attachment to rods. Grounds and neutrals separate buss bars. Can bonded to ground.
thanks
Privately metering a tenant is prohibited is illegal in many areas. If allowed, doubtful, charging anything over actual usage is illegal.
Does your tenant have access to his/her breakers?
Code05 is offline   Reply With Quote
Old 07-15-2012, 01:19 PM   #4
Code05's Avatar
No need to bond sub panel to water pipe. 4 wire feed is all that is needed.
Adding subpanel next to main box insane_drummer Electrical 25 06-10-2011 10:39 AM
Adding a subpanel to a sub-panel and other questions CardinalPilot Electrical 14 03-30-2011 02:23 PM
Another subpanel question:) primal65 Electrical 15 06-22-2008 09:43 AM
Subpanel installation in outbuilding fls Electrical 19 03-16-2008 02:19 PM
Reverse Polarity at the Subpanel adm060306 Electrical 14 07-09-2007 12:58 PM