Originally Posted by chris75 View Post
Everyone has to remember that the NEC is pretty much minimum, and a breaker tripping is really not a safety concern, maybe an inconvenience, but it will not start your house on fire. I hope everyone understands the exceptions to this code, and if you do not PLEASE ask...
Chris,
Let's proceed from here. Will you explain the exceptions?
Andy in ATL is offline   Reply With Quote
Old 01-13-2008, 07:38 PM   #32
Electrician
Originally Posted by Andy in ATL View Post
Chris,
Wrong choice of words on my part sorry, I just wanted everyone to know that in order to use a 20 amp receptace on a 15 amp circuit you must first be using a single receptacle on a individual branch circuit...
chris75 is offline   Reply With Quote
Old 01-13-2008, 07:38 PM   #33
Electrician
Chris,
Double post.
Old 01-13-2008, 08:00 PM   #34
I guess where my brain is twisted is on my exp. wiring the typical dwelling unit . I always ran a dedicated 20A rect to beat the GFCI rule in basements. Rule goes away in '08. My head hurts.
Old 01-13-2008, 08:06 PM   #35
Electrician
Alot of good rules go away in 08...
Old 01-14-2008, 06:21 AM   #36
waiting for spring
arichard21's Avatar
Rewards Points: 150
So now that the great debate is over, can anyone else weigh in on the issue of why recepticles aren't designed with 2 ground screws to feed through like the hot and neutral?
arichard21 is offline   Reply With Quote
Old 01-14-2008, 06:45 AM   #37
Electrician
Its already been answered, because of a continuity issue.
The arrangement of the grounding connections shall be such that the disconnection or the removal of a receptacle, luminaire, or other device fed from the box will not interfere with or interrupt the grounding continuity.
Old 01-14-2008, 07:11 AM   #38
waiting for spring
arichard21's Avatar
Rewards Points: 150
I understand you answered this from a CODE standpoint. That is not what I am looking for. I want to know from the people who work in the trade as to why it was never developed this way in the first place.
I guess I am not going to get anywhere with it.
Old 01-14-2008, 07:44 AM   #39
Licensed Pro
It was never developed this way because of the continuity issue.
Old 01-14-2008, 10:13 AM   #40
Rewards Points: 1,548
With the ground back to the panel and the continuing ground on separate screws, it is easy to break the ground continuity without thinking about it and forget to reconnect it. Whereas with the ground wires fastened directly to one another, disassembling the ground at least has to be a conscious and pro-active maneuver.
It is true that all ground wires coming into a box are to be tied together. Still, it is required that in new construction that a ground wire accompany the feed in the same cable or conduit back to the panel as opposed to relying on a ground going back to the panel via a different physical routing.
Old 01-14-2008, 03:29 PM   #41
Electrician
I work in the trade, and to answer your question as simple as I can, because its a dangerous method. and the NEC would never allow it to be developed that way.
Old 01-14-2008, 04:27 PM   #42
Res Ipsa Loquitur
Coincidentally- this is the same reason I like to use pigtails for continuous runs of hot and neutral as well rather than the separate screws.
handyman78 is offline   Reply With Quote
Old 01-14-2008, 04:28 PM   #43
Rewards Points: 344
Hey ARichard - now the the Quick Questions are answered - how about a couple Loooong ones ?
No offense to anyone intended !
tribe_fan is online now   Reply With Quote
Old 01-14-2008, 05:34 PM   #44
Electrician
Sometimes you have to take the long way home...
Old 01-14-2008, 05:55 PM   #45
"Low impedance path"
That is our goal as pro's. How can I, as a pro who understands Grounding and Bonding, speed the path back to the source in the case of a ground fault? I work very hard at it. Continuity is key.
I have a problem with the new MC all purpose. You don't technically have to bond a device if you remove the retaining clip on the device or purchase self grounding devices. I see continuity issues here. Granted, It would never be a danger if we all LOTO.
Aluminum-wired house, questions LMH Electrical 2 05-24-2009 03:06 AM
tiling questions - in middle of install mwill Flooring 8 12-11-2007 05:06 PM
Another quick questions for the experts keyser soze Electrical 22 05-31-2007 07:32 AM
Two quick questions?? t-nutsaz HVAC 2 07-21-2006 01:16 PM
How many recepticles Barry Electrical 7 12-14-2005 10:20 PM