In a recent post I learned you could not use a tandem 20A breaker for 10-3 UF because the one neutral wire would be overloaded. I am confused about this. They said the problem would be eliminated if I used 2 single 20A breakers which would split the hots over 2 seperate poles. I understand that part but there still is just one neutral wire. Would I pigtail this to two seperate neutral bars? Please help me understand the what to do and why of this issue at the 200A house panel and the small panel I will use at the shed. Thank you.
Joe Willie is offline   Reply With Quote
Old 05-06-2011, 07:32 AM   #2
joed's Avatar
Rewards Points: 13,766
When you split the hot across the two legs the neutral only caries the difference in current. Example one hot pulls 10 amps and the other pulls 5 amps the neutral only carries 5 amps.
If both hots are on the same leg, which they are with tandems, the neutral carries the sum of the currents. In the above example the neutral would be carrying 15 amps.
Old 05-06-2011, 07:34 AM   #3
Lic Elect/Inspector/CPO
The service has two conductors and bus bars are 180 degrees out of “phase” and can be understood by visualizing two waves running together where the trough of one wave is opposed by the crest of the other wave. Thus these waves are able to travel on the same wire without creating any problem (as in the top half of the picture below).
How the waves of a muti-wire circuit work
Here is where the trouble can start—when the two circuits share the SAME bus bars (as in the bottom half of the picture above). The neutral wire can now be required to carry the possible full load of both circuits on the same wave length—-30 amps—-and the wire is only rated for 15 amps. Insulation starts to melt from overheating and the risk of an electrical fire increases when this happens.
To make it easier to wire breakers in the electrical panel the bus bars are configured like fingers such that every other breaker space is a different bus bar. Most electrical panels have breakers that increase the capacity of the panel by having two breakers in each of these spaces—-this is usually where the mix-up occurs and the two hot conductors end up on the same
NJMarine is offline   Reply With Quote
Old 05-06-2011, 09:02 AM   #4
Thanks. I understand now. Can I use the tandem out at the shop panel (I plan on purchasing a small 4 or 6 space box)? I only plan on needing 12 amps (fridge and lights) on one circuit and 15 amps (small tool or small AC) on the other.
Old 05-06-2011, 11:39 AM   #5
I=E/R
a7ecorsair's Avatar
It isn't the wire size, it is how the wiring is connected. You can use tandem breakers as long as each circuit leaving the panel has only a hot and a neutral.
a7ecorsair is offline   Reply With Quote
Old 05-06-2011, 11:43 AM   #6
Thanks.
Old 05-06-2011, 03:16 PM   #7
walt1122
Rewards Points: 334
instead of the tandem can't he just use a double throw breaker and insure that there are two seperate hot legs. If this is to supply the shed? shouldn't this be treated as a sub panel? How far away is the shed? What will it power?
thanks
Walt
walt1122 is offline   Reply With Quote
Old 05-06-2011, 04:50 PM   #8
Rewards Points: 1,548
Since you are running a 10-3 cable, you can use a double 30 amp breaker at the source (either a main panel or a subpanel) but you will need at subpanel at the destination end (garage, shed)
If you feed the cable with a 15 or 20 amp breaker, you don't need a subpanel at the other end; just a box with receptacles will suffice.
If you already bought the tandem breaker (single wide, occupies one slot), you can use it in a subpanel at the destination end of your 10-3 cable provided that the breaker is compatible with the make and model of subpanel. It would feed circuits wired with 12-2 cable. You could also use it back at the main panel for other circuits wired with 12-2 cable, in order to free up a slot in the panel for something else.
Usually there is just one neutral bus (bar) in a panel and the neutral from the 10-3 cable goes there and ithere is no problem connecting the red and black wires to the double wide (2-slot) double breaker.
If there are two neutral busses (not ground busses) they are interconnected and you connect the neutral wire to just one, usually the closest.
Old 05-06-2011, 05:13 PM   #9
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,276
He will also need a disconnect for this MWBC, a pair of single pole switches will do.
Coastal South Carolina
Old 05-06-2011, 09:13 PM   #10
" Euro " electrician
frenchelectrican's Avatar
Not all area will approve it and I know few spot in Wisconsin I have dealt with it before they will required double pole switch for MWBC.
Merci,
Marc
Multi Wire Branch Circuit MWBC w/4X or 6X hots or more, 1X oversized neutral mysterylectric Electrical 7 05-05-2011 10:16 PM
Induction Cooktop, no neutral (?!) andersol Electrical 7 09-28-2010 03:47 PM
question on the "stubbie" bonding links n175h Electrical 12 10-13-2009 04:09 PM
Main disconnect neutral wiring Daniel Holzman Electrical 5 10-04-2009 01:36 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 04:58 PM