2 ground rods for homes in tx
I only have one gr rod for my home I live in Bryan tx I don't know a lot about it and I've never heard of 2 gd rods here what is the purpose of 2 I've been hearing y'all talk about.
Unless it can be proved that the one rod is enough to get the resistance down below 25 ohms the code requires an additional electrode. It is easier to drive two rods and be down with it and avoid the need to show the inspector your testing of the one rod.
Once the second electrode is driven there is no requirement to keep adding electrodes to get below 25 ohms. |
I believe the 2 ground rods were decided as an alternate to the one.with just one rod,code requires a rather expensive test to determine if it will fall below a certain #. I think 2 rods will not give you any more protection then the one you already have.
I have only one myself. It was inspected when I did the service upgrade about 15 years ago. I have no intentions to install another one, nor am I required to.
Two ground rods will lower the effective resistance to ground, thus providing a more conductive path. For example, if each ground rod is 30 ohms, two ground rods in parallel will present a resistance of 15 ohms. The lower the resistance, the more current will flow to ground, as opposed to some alternate path.
this and other recent ground rod discussions prompts me to ask the following question. If a service is bonded to an incoming copper water service, is any better protection provided by one or more ground rods? In my case the water service is about 40 feet away from the service entrance panel and any additional ground rods would be within a couple of feet of the panel. I understand that the cold water service ground met the code when the house was built in 1985. The copper water service is about 50 feet long to the street which is a cast iron main.
bernie |
Look up your power company provider web site on installation requirements.They require us to use 2 rods at least 6 feet apart,no asterick about only 1 if you can show 1 rod does the job. This is for new installs of course,not existing.
I should ask, if the building has an entering water pipe or a concrete reinforcing bar as a grounding electrode, is just one ground rod sufficient?
Note: There is some issues that do arise with Ufers. Some people will tell you that all you need to do is bond to the Ufer and nothing else. However, in my area, the Ufer only takes the place of the rods, and you will have to bond to water if present. |