2 Breakers, 1 Circuit - Confused - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 11-20-2011, 10:21 PM   #16
joed's Avatar
Rewards Points: 13,712
Originally Posted by mpoulton View Post
I bet one breaker is on the feeder for the other panel. That's the only situation that makes sense. Check to see if one breaker turns the entire other panel on and off.
That makes sense. The two breakers must be in series. One is feeding the other which is feeding the circuit. The feeder breaker must feed more than just this one breaker.
Turn off one breaker and measure the voltage at the output of the 2nd breaker. If there is voltage at the 2nd breaker then the 2nd breaker must be the feeder.
What are the breaker values?
Old 11-21-2011, 03:51 AM   #17
dmxtothemax's Avatar
Rewards Points: 5,604
If it is a 240v circuit ?
Are not the two breakers meant to be linked ?
So you should not have two breakers in different panels ?
Most likely NOT code compliant !
dmxtothemax is offline   Reply With Quote
One circuit, two breakers? billinak Electrical 15 08-09-2012 06:11 AM
1 neutral; 2 circuit breakers readar Electrical 12 07-24-2011 09:58 PM
Arc fault circuit breakers bkvanbek Electrical 6 06-10-2011 11:39 AM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
Just for fun Andy in ATL Electrical 56 10-20-2009 09:33 AM