Hi all,
I am doing a master bath renovation and ran a 12/3 bx cable up to the bathroom. One 20A circuit to feed our new tub and one 20a circuit to feed our in floor electric heat. Obviously i want to protect these two circuits with GFCI breakers, however before hooking up the neutral the wrong way I want to ask here. I was thinking to run the curly wire from each breaker to the neutral bar, Then run the neutral from the 3 wire cable to one breaker, and then run a wire from the neutral of one breaker to the neutral of the other (basically jumping the neutral and having two neutral wires going into one breaker) - is this the right way? the other option I guess is to tie my neutral to two wires and make two "pigtails" in the panel - bringing one neutral to each of the breakers.
Any advice is much appreciated...
thank you!!!
jbfan 10-02-2012 12:11 PM
It will not work with induvidual breakers.
You need a 2 pole breaker, or you need gfci receptacles.
Your single pole gfci breaker will trip with the shared neutrals.
mazzonetv 10-02-2012 12:22 PM
Thank you for such a quick answer! Much appreciated! Would it be ok to put one circuit (for my floor heat) on a gfci breaker and the other circuit for my tub on a gfci outlet - or is that essentially doing the same thing? If I used a 2 pole gfci breaker would that be a better solution? Should I just bring up another 2 wire cable and call it a day?
jbfan 10-02-2012 12:25 PM
That would be essentially the same thing.
A 2 pole gfci breaker is expensive, so if the walls are still open, I would opt. for another cable.
mazzonetv 10-02-2012 12:34 PM
Thanks - not the answer I wanted but glad I checked!! I guess I'm running another cable tonight...
Appreciate the advice!