-   -   190 185 voltage ? (http://www.diychatroom.com/f18/190-185-voltage-88302/)
PIGEONS 12-01-2010 12:35 PM
190 185 voltage ?
THIS ALL STARTED OUT WHEN THE ELECTRIC DRYER 30 AMP 220 VOLT
WAS NOT HEATING UP. The Appliance Guy said, the Dryer is A - OK,
it is a electrical problem. So, finally out came a digital voltage tester,
and one hot leg of the Dryer Outlet reads 185 volts, the other hot leg
reads at zero. So, I went and opened up the circuit breaker box, it
is inside, and this by the way is a Manufactured Home, I checked the
two Hot wires coming out of the 2 pole 30 amp c/b and they both read
this weird voltage of 185. Then, just to check other goings on, I found that each and every circuit breaker has 185 volts coming out to
everything in the House, I checked a regular wall outlet, it gave me a
a whopping 190 volts reading. wow, then for further investigation
I went out some distance from the Manufactured home, and discovered
the out lets read 160 volts, now how long all of this has been going on
I am not sure, The main reason for checking out any of this was the fact that the Dryer didn't heat up, last detail, we know the 2 pole
30 am dryer c / b is working, but the one Hot wire which happens to be
RED, is not working, is this the culprit of all this rather high voltage,
could this Red wire be shorted out, and some how back feeding everything, making all voltages higher, or can you tell me what
else could be the cause, also, is this dangerous to the occupants. ?
I have never encountered such a voltage reading, thanks PIGEONS
McSteve 12-01-2010 12:43 PM
As a precaution, turn off everything. Then put fresh batteries in your meter, I've seen them read high when the batteries are low.
If you still have weird voltages, call the power company out to check their side of things. If the voltages are really that high, it could damage appliances and equipment.
nap 12-01-2010 02:53 PM
turn off the main breaker and check the voltages at the incoming line, both legs to neutral and then leg to leg. You should have 120/120/240 +- 10% (max but some states limit it to 5%). If above or below those readings, or really if even close, I would call the power company.
a7ecorsair 12-01-2010 04:45 PM
It's nice that you have a digital meter but your approach to this problem is incorrect. The dryer is primarily a 240 volt appliance so stop measuring voltage from each leg to ground until you know if you have full voltage between the two to legs. If you don't have 240 at the dryer breaker, then move to the main disconnect. If you don't have 240 at the main disconnect then call the poco.
If you have 240 then you can check from each leg to neutral and/or ground. If your 120 reading are strange then you have a neutral problem which could still be a poco problem.
McSteve 12-01-2010 05:19 PM
Yeah, this is a weird one. The way I read it is that he has lost one leg at the drier outlet for sure, and in troubleshooting he's found about 185v to ground at multiple circuits on both legs, so I'm not thinking it's a neutral problem. Sounds like either a faulty voltmeter, or a serious power company issue.
I hope he gets back to us soon, the weird problems are always interesting...
PIGEONS 12-02-2010 10:07 AM
the weird 185 -- 190 voltage's
to all that have answered, first, you are correct,
the Digital Voltage meter had Low battery, and that is why the
super unusual high voltage readings, with New 9 v battery the
outlets read 116 volts, which is a good thing.
We will be doing some more testing today, as many of you suggested different approaches, but, one thing for sure, Yes, it seems that
we have lost one leg to the Drier outlet. We have juice coming out of
both legs of the Circuit breaker ( 2 pole 30 amp ) but at the out let
only one leg is Hot. No wonder the Dryer wasn't heating up.
Will get back with more later, PIGEONS
J. V. 12-02-2010 10:54 AM
Great point. There is rarely ever a reason to be checking anything to ground except when working on your car or truck. This "well I read this to ground" immediately tells me the operator of the meter or voltage tester has no idea of what they are doing. ALWAYS ALWAYS read the across the conductors that supply the power to the load.
There are times as professionals we read to ground for certain reasons. DIY'ers have no reason to read to ground, unless they want to verify there is a ground. Good post.
Low batteries have no effect on meter voltage readings. Its very simple. Check across the two hot wires. If you have 230-240 volts you have the correct power. If you can check this voltage reading with a load on the circuit it will prove it. Voltage readings are not always accurate unless the full load is applied.
Unless you plan to work in the industrial electrical field, put away your digital meter and get a solenoid tester. You don't make assumptions with solenoid testers. Besides, they use no batteries.
McSteve 12-02-2010 11:17 AM
Originally Posted by J. V. (Post 544265)
Low batteries have no effect on meter voltage readings...
Actually, this may be true for the nicer Fluke and etc. meters, but this seems to happen a lot with the cheapos. We had another thread fairly recently where someone was reading about 20-40 volts high due to a low battery. My spare crappy CAT-zilch meter does the same thing. Just throwing it out there for future reference.
walt1122 12-06-2010 04:57 PM
just my 2 cents.
Had a similar problem with the whole house. One leg would show 160V while other side was 95V. Turn on a light or appliance and the numbers would change drastically. Flourescent lights in basement were so bright you had to wear sunglasses. Switch on some light somewhere and the basement lights went dim.
Electric company told me it was something I had done that made it behave that way till I removed ALL the breakers ( no load) and showed them it was the lugs at the panel BEFORE the main that were still showing these screwed up voltages.
Conclusion: the ground back to the street was broken and the voltages floated back and fourth between the two legs. But between the two legs you got 240V. They replaced the ground and that fixed it.
Walt
McSteve 12-06-2010 04:59 PM
Yep, that's the classic loose/broken neutral scenario. Glad you got it fixed; that'll toast electronics in a hurry.
caal 12-21-2010 11:45 AM
So whats the conclusion to your problem Pigeon.