im changing my old black recepticals to white ones and i notice on my countertop outlets the recepticals (old ones) say 15a. but the breaker they are on is 20amp. is it ok that i change the old black 15a receptical to a white 15a on the same 20amp breaker?
Scuba_Dave 03-04-2009 07:51 PM
Yes, as long as it is a duplex - 2 places to plug a device in, VS only a single place to plug a device in
15a passes thru 20a
micromind 03-04-2009 08:27 PM
The code reference here is Table 210.21(B)(3).
It plainly states that with a circuit (breaker) rating of 20 amps, the receptacle rating can be 15 or 20 amps.
The entire table applies only to circuits that have two or more receptacles. A duplex is two receptacles.
210.21(B)(1) prohibits the installation of a single receptacle on a circuit greater than the rating of the receptacle.
Rob
sweaty 03-04-2009 10:04 PM
The nice thing about using 20A receptacles is that it gives you a visual indicator of the higher capacity circuit.
jbfan 03-04-2009 10:23 PM
And is a complete waste of money!:thumbup:
sweaty 03-05-2009 12:03 PM
Why are they a complete waste of money?
hpp58 03-05-2009 12:14 PM
A 20 amp plug will not fit into a 15 amp receptacle.
(how many time has the average home owner even seen a 20 amp plug, maybe a AC unit)
When you have a need for a 20 amp appliance it should be on it's own circuit.
This way you only use 20 amp receptacles for dedicated circuits.
Use 15 amps for everything else
rgsgww 03-05-2009 12:17 PM
I agree with hpp. Most 20a appliances pull about 16 amps. There isn't much room after that.
fabian 03-05-2009 12:21 PM
thanks for the reply to my question. im always learning!
Scuba_Dave 03-05-2009 12:32 PM
I buy Pro - heavy duty receptacles
The 20a were about the same price as the 15a
So I bought the 20a
Now under NEC 2008 all receptacles must be tamper proof
Outside must be GFCI & weather proof
Outlets have more then doubled in price :(
I'll probably swap the 20's out to the garage