120V Subpannel? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-17-2011, 12:28 PM   #1
Rewards Points: 194
120V Subpannel?
I posted on this issue before but didn't realize the my current subpanel is only 120V. Here is a quick summary of what I'm doing:
I am moving a wall that currently contains an old subpanel. I will put in a new subpanel on the new wall and will run a new feed wire from the main as well as new wires to the first junction boxes downstream (that's a term we use in the water industry, not sure if it translates to electrical industry) of the subpanel.
I've researched subpanel topics on this website and it seems that all of them are 240 volts. My problem is that my current subpanel is only 120 volts and it is fed from a 30 amp breaker in my main. Attached is a picture of my main and the wiring diagram. Is there a way for me to rearrange my breakers so that I can get 240 to my subpanel? If not, does it really matter if my subpanel is only 120? I'm not changing or adding any load - I'm just upgrading the panel and some wires.
Also, I showed what I've changed since taking the picture. I connected two of the breakers together (they weren't when the picture was taken), and I changed the two 50-amp breakers to two 30-amp breakers for my dryer. Not sure why they were 50-amp before.
Thanks!
And here is the old subpanel that I am replacing
loftezy is offline   Reply With Quote
Old 05-17-2011, 12:45 PM   #2
Rewards Points: 1,418
The first thing you need to convert a 120 volt subpanel to 120/240 volts is another hot wire. Practically you need to run a new cable with 3 conductors plus ground.
On a typical panel, a double wide breaker will give you 120/240 volts but not all possible positionings in the panel will work for all brands of panels. You can move a single breaker up or down to get a pair of slots that give 240 volts for the double wide breaker. In your case you might move the lower left breaker to the top left and put the subpanel breaker set at the lower left. Measure the voltage between the two fins in the adjacent vacant slots to be sure you get 240 volts.
Old 05-17-2011, 12:48 PM   #3
I=E/R
a7ecorsair's Avatar
Move all the breakers on the left column up one space or down one space and you should have a place for a two pole breaker.
a7ecorsair is offline   Reply With Quote
Old 05-17-2011, 02:00 PM   #4
Rewards Points: 194
Thanks for the tips - it seems easy enough!
By the way, on the wiring diagram, what do the different number of lines mean? For example, 1 2 3 and 4 come off of one line but 5 and 7 are two lines that branch off of one. Do those lines indicate where I can have two pole breakers or do they show where I can have mini breakers?
Old 05-17-2011, 02:54 PM   #5
Rewards Points: 506
What diagram? I don't see one here
Old 05-17-2011, 04:02 PM   #6
Rewards Points: 194
The diagram is the first picture shown. It is from the label on the cover to my main panel.
Old 05-17-2011, 04:34 PM   #7
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,034
Diagram shows where you can use the slim (mini) breakers; 1-4 are full size only, the rest are full or slim.
You panel is a mess, take the time to clean it up. Splice the wires out to make them longer so the wires stay out at the edges of the panel and not run across the face. Don't make the wires too long so that you have to deal with a bunch of slack.That cable sheath should not be in the box, strip it back to the NM cable connector.
Coastal South Carolina
Old 05-17-2011, 04:53 PM   #8
Rewards Points: 194
I think you are right - a good cleaning is definitely needed!
Old 05-17-2011, 06:48 PM   #9
Rewards Points: 194
So, here's the plan:
- Move all the breakers on the left side of the main down one slot to make room for a two pole breaker.
- Install 60 amp two pole breaker at main.There isn't a need to upgrade but I figured I might as well since I'm running new feeder wire.
- Run new 6/3 copper to new subpanel
- Install new flush mount subpanel inside
- Make sure that ground and neutral in subpanel are separated
- Install new breakers (AFCI as needed) in subpanel
- Run new wires to first junction boxes off of subpanel
- stand on a wood chair, say three hail mary's, close my eyes, and flip the breaker.
Anything else?
Old 05-17-2011, 07:00 PM   #10
A "Handy Husband"
rjniles's Avatar
Do it right and take your time and this will not be necessary. Before I activate a new circuit, I take the time to use a multimeter (ohmmeter) and make sure there are no grounds or shorts any place not called for. No continuity between the hot conductors or from the hot conductors to ground and neutral.
switch from 120v to 240v new breaker popwarfour Electrical 24 04-28-2011 09:17 PM
converting a compressor to run on 120v wizz1022 Electrical 1 05-04-2010 05:30 PM
Pulling 120V outlet from a 240V circuit? npage148 Electrical 12 11-08-2009 12:29 PM
Do you think a tool running at 240v works better than at 120v? Piedmont Electrical 39 07-03-2009 10:50 PM
Understanding 120V branch loads in 100A 240V system WaldenL Electrical 17 02-17-2009 10:15 AM