Originally Posted by rgsgww View Post
Its just because computer equipment will be on the circuits, and that they will be connected together. I dont want the voltage difference. Computer PSUs and mwbc don't mix very well.
I am thinking about a load center because I'm getting tight on space.
And what makes you believe this?
chris75 is offline   Reply With Quote
Old 01-28-2009, 08:29 PM   #17
Some psus are nonlinear loads. Id like to avoid a mwbc.
rgsgww is offline   Reply With Quote
Old 01-28-2009, 09:33 PM   #18
Rewards Points: 266
rgsgww,
Question for ya
I remember reading this thread:
Messy electrical, NOT DIY
It looks like you have plenty of spaces left for your circuits in your panels. Why not just run them from there? You could have them on the same leg if you want. The other thing is what size feeder would would you run? Single pole breakers above 30 amp are not usually available at the big box store, unless you stick in a double pole and only use half.
Curious
junkcollector is offline   Reply With Quote
Old 01-28-2009, 09:46 PM   #19
Electrical Contractor
jbfan's Avatar
Rewards Points: 138
REALLY?
Ever walk into an office building?
A computer room.
All wired with mwbc's every day, all day long!
jbfan is online now   Reply With Quote
Old 01-28-2009, 09:52 PM   #20
Originally Posted by junkcollector View Post
rgsgww,
Question for ya
Curious
I think I might just use the panel. If I went the sub way I'd probably use flex conduit (its only going to be a few inches from the panel) and 6 awg thhn. 60 amp breaker would protect this.
My labels are messed up after I cleaned 5 spaces of unused breakers. I found a 12/3 from 1980 cut clean and it was live! I think It fed a pool.
Old 01-28-2009, 09:57 PM   #21
Originally Posted by jbfan View Post
REALLY?
A computer room.
I think I'm going a little overboard with my wiring! Since my psu is fairly new (2007) I doubt is has harmonics, if at all.
I don't like the voltage difference (I want to spread my equipment out) across everything.
Old 01-28-2009, 10:09 PM   #22
Rewards Points: 506
Send a message via AIM to theatretch85
I actually bought a box of 10 Square D QO single Pole 50 amp breakers. I have used them for several sub panels in a temporary setup at 120 volts for computer LAN parties. 50 amp panel feeds 24 computers with 4 15amp circuits. As far as running the panels at 120 volts, we simply used a piece of 6 gauge wire to jumper between the two legs of the sub panel, which meant we had one lug with 2 wires under it. Your other option would be to jumper the two legs in the panel, and feed it with a backfed breaker; of course for it to be legal you'd need a hold down kit for the main breaker in the panel.
FYI- the single pole 50 amp breakers are "QO150"
theatretch85 is offline   Reply With Quote
Old 01-29-2009, 12:23 AM   #23
Idiot Emeritus
Rewards Points: 1,492
Harmonics are not much of an issue in a single-phase system. They tend to cancel each other out on opposite phases.
In a 3 phase wye connected system, harmonics will cancel each other when connected line-to-line, but will magnify in a line-to-neutral connection. The only real issue here is excessive neutral current.
Rob
micromind is offline   Reply With Quote
Old 01-29-2009, 08:05 AM   #24
Rob
I remember reading about wye systems and server rooms. Harmonics was an issue with excessive neutral current.
I wasn't worried about harmonics because I have a single-phase or "split-phase" system. I just didn't want the voltage difference across my equipment.
Old 01-29-2009, 10:06 AM   #25
Are you talking about voltage difference between each leg of the system?
jerryh3 is offline   Reply With Quote
Old 01-29-2009, 12:00 PM   #26
Yes. If I ran a mwbc then it would need two different legs. Since I don't want that, I diddn't run 12/3.
Old 01-29-2009, 12:16 PM   #27
Wouldn't everything be going on UPS with a voltage regulator anyway? I don't see how a volt or two between each leg would make much of a difference. What kind of equipment are we talking about here?
Old 01-29-2009, 12:24 PM   #28
DIYer
If you are running a lot of SMPS, the main thing would be to find a way to avoid putting it on anything with ground fault protection. A whole room full of computers can easily leak enough to trip GFCIs. People are also reporting lots of AFCI nuisance tripping with some big server power supplies, so definitely plan for the future so you never have to upgrade this once you are saddled with 2008 NEC.
Gigs is offline   Reply With Quote
Old 01-29-2009, 12:29 PM   #29
Im not going to put it on a ups, it would cost alot of money.
Just basic computer components, psu, monitor, networking equipment, sound amp. The psu pulls a max of 1600 watts. Finding a ups for that would be hard.
Im going to put the stuff on 2 of these
http://www.dale-electric.com/detail?itemnumber=8380-W
I need a 20 amp power strip, so I might just make one out of these
http://www.dale-electric.com/detail?itemnumber=8300-HR
Termite repair to load center wall - precautions shepiii Electrical 3 01-21-2009 05:14 PM
CH42B200R Load Center for Detached Home Theater nomad4137 Electrical 6 07-21-2008 07:57 PM
Main Load center Size Evnldr Electrical 11 06-13-2008 11:10 PM
Load Center dwayne Electrical 4 07-09-2006 02:02 PM
100A load center run Littlefatdog Electrical 12 06-15-2006 03:31 AM