120/208v Coffee Maker Hook-up ? - Electrical - DIY Chatroom Home Improvement Forum
Old 04-25-2010, 04:39 PM   #1
120/208v coffee maker hook-up ?
My church had a coffee maker donated to them by a local convenience store. This joker is big. The name plate states 120/208V 28.7A single phase 3 wire. There is no motor so I am assuming I will need a 40A circuit to protect it? Any one? I've been out of the business a few years so be gentle
Andy-n-ATL is offline   Reply With Quote
Old 04-25-2010, 04:59 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
You could get away with a 30A circuit, but you may feel better with a 40A.
Be careful about the circuit. You will likely need to use MC cable or all conduit and wire as this is a place of assembly, although the kitchen may be exempt.
I'd use at least MC cable in any case.
Old 04-25-2010, 05:03 PM   #3
Bahh!!! How could I get away with 30A if the max allowable is only 24A on a 30A circuit? What am I missing? No worries on a code compliant installation BTW, I just wanna get the breaker size right
Old 04-25-2010, 05:13 PM   #4
The 29A is for when it's wired to run on 120v?
Old 04-25-2010, 05:26 PM   #5
Master Electrician
Rewards Points: 3,870
The maximum allowable load on a 30 amp circuit is 30 amps. The continuous load of 3 hours or more is limited to 24 amps on a 30 amp circuit.
brric is online now   Reply With Quote
The Following 3 Users Say Thank You to brric For This Useful Post:
frenchelectrican (04-26-2010), Scuba_Dave (04-25-2010), Speedy Petey (04-25-2010)
Old 04-25-2010, 05:35 PM   #6
Gotcha, I'll just pipe some # ten over and make up a cord with a twistlock. Thanks guys.
Old 04-25-2010, 05:37 PM   #7
Hey, anyone wanna give me a NEMA configuration real quick??
Old 04-25-2010, 05:46 PM   #8
A-ha Grasshopper. This is a myth long perpetuated by those not knowing the actual code.
Exactly.
Old 04-25-2010, 05:47 PM   #9
Originally Posted by andy-n-atl View Post
hey, anyone wanna give me a nema configuration real quick??
l14-30
Last edited by Speedy Petey; 04-25-2010 at 05:48 PM. Reason: It will absolutely not let me capitalize that "L". :(
Old 04-25-2010, 05:50 PM   #10
No, the amperage rating would be total at the higher voltage.
A lot of these machines are 120/240 or 120/208 rated for some reason. Not sure why they would need the 120.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Yoyizit (04-25-2010)
Old 04-25-2010, 05:54 PM   #11
Idiot Emeritus
Rewards Points: 1,492
If and only if it's a single receptacle, you'll be fine with a 30 amp breaker and #10 wire for any load up to 30 amps.
The receptacle will be a NEMA 14-30 for straight blade (same as a 4 wire dryer), or an L14-30 if you want a twist-lock.
You'll need two hots, a neutral, and a ground.
Rob
micromind is offline   Reply With Quote
Old 04-25-2010, 05:57 PM   #12
Electrical Contractor
jbfan's Avatar
Rewards Points: 478
That you Andy, from the past Andy?
jbfan is online now   Reply With Quote
Old 04-25-2010, 06:02 PM   #13
LOL it is. Sorry for the confusion on my part guys, its just been awhile and my laziness leads me here to get good answers with minimium effort on my part. I peeked in it really quick this morning and im not convinced its got a neutral. It came out of a Quick Trip so its bad a##. What ya think?
Old 04-25-2010, 06:06 PM   #14
Idiot Emeritus
If it states 120/208-230, then it will have a connection for the neutral.
If it's 208-230, then it doesn't need the neutral, and you'll only need two hots and a ground.
A lot of these machines need the neutral for the controls, just like a dryer.
Some of these machines have 4 terminals/wires. Two for the 208 or 240, and two for the 120. This way, if the service is a 240 delta, you can use the high leg.
Rob
The Following User Says Thank You to micromind For This Useful Post:
Old 04-25-2010, 06:19 PM   #15
Gotcha. I should amend that it has a hot water faucet as well, which INHO would qualify it as a continous load correct?
hook up ice maker line. already have a valve on the floor behind fridge but...3/8" bakchoi Plumbing 5 11-25-2008 06:59 AM
Ice Maker Not Getting Water sgorak General DIY Discussions 3 10-27-2008 08:02 PM
Kenmore ice maker acting strange BJLower Appliances 3 10-24-2008 11:14 PM
Ice Maker problem. sflamedic Appliances 5 08-25-2008 05:28 AM
Can I pipe my ice maker off my RO unit? Leah Frances Plumbing 10 04-24-2008 06:44 PM