So what I'm saying is that one pole of the double pole (green) and that 1/2" single pole share the same bus tab same thing with the 1/2" single pole above the new (green double pole). But you do create two 1/2" single pole spaces...one above and one below the new 1/2 size double.
Would that be a "problem" then? What are the implications of doing this?
unixb0y is offline   Reply With Quote
Old 03-11-2009, 11:20 AM   #17
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
It appears to be a 16/32 panel as it is configured so it will take 16 full size or 32 half size breakers.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 03-11-2009, 11:22 AM   #18
UAW SKILLED TRADES
Stubbie's Avatar
Its no problem at all...just pointing out that the 1/2" doubles install in 1/2 of two different bus stabs.
Stubbie
Old 03-11-2009, 11:27 AM   #19
I wonder why they would design it that way.
Old 03-11-2009, 12:14 PM   #20
UAW SKILLED TRADES
Stubbie's Avatar
Other manufacturers do the same thing, it allows you to install a double pole breaker in situations where you cannot fit a full size and provides for more single pole spaces for 120 volt branch circuits. Take your panel at present it is full. If I take out the two full size doubles on the top left and bottom left column and replace them with 1/2 size doubles I will create 4 spaces for 120 volt branch circuits.
Stubbie
Understanding 120V branch loads in 100A 240V system WaldenL Electrical 17 02-17-2009 09:15 AM
Basement Renovation Question KUIPORNG Remodeling 234 08-26-2008 08:19 AM
New service Question Onytay Electrical 1 10-24-2007 05:47 AM
One furnace question and one thermostat question lh0628 HVAC 4 10-11-2007 10:17 PM
Wiring 100A subpanel nebulous Electrical 9 08-29-2007 02:41 PM