Is 1000 watt power supply unit safe on home socket?
Is a 1000 watt power supply unit safe to run on a home socket? Since home voltage is 120, and 120 V X 8 amps = 960 watts, I think that it is. But I want to check to be sure.
Thanks |
A socket should supply 15 amps so that is 1800watts so you should be good. If you are talking about a computer power supply, it will only draw it's maximum wattage to charge the capacitor then it wont be using that much (unless all the components do add up to that much, but most likely not, the wattage is just it's capacity).
You can have like 5 pcs running off one socket no problem, just don't plug them all on at once, and even then think you'd be fine as the draw surge would be very short. |
Yes it is a computer psu. Thanks for the info.
Bad info!
While some of the information Red Squirrel provided was accurate - conversion of amps to watts - the remainder is not. The amperage rating of the receptacle has noting to do with the ampacity of an existing circuit and is not the parameter that needs to be considered to prevent overloading of a circuit! The rated ampacity of the existing circuit breaker/fuse, the size of the wire running from the panel to the existing receptacle, and the existing load on the circuit are the parameters to be considered. 1000 watts |
If the plug gets hot with this load the socket is worn out. |
Wife's vacuum pulls 12a & she plugs it in all over the house
Now if we had a PC pulling 1000w & she plugged the Vac into the same circuit a 15a breaker would trip. A 20a can handle up to 2400w, so it would be close if there were other loads on the circuit So verify where you will be plugging it in & other loads I always have a UPS that my PC plugs into |
True, but if everything is to code, a 15 amp socket should have wire capable of handling 15 amps or more. At least, I would think. I'm not an electrician. |
\ If this were my house, I'd run a dedicated 15 amp circuit for the power supply. |
While checking the place out after moving in I found that speaker wire had been used to put outlets in the last room It was probably done long before heavy electric use But it was still there |
I ran my furnace and a couple of lights on a 1250W, 100 dollar generator from Big Lots last January for almost a week after an ice storm, so, yeah, you should be fine. (My house furnace blower draws about 6 amps.)
Let me tell you, I didn't mind being in the dark (mostly) when the house furnace (natural gas) was working. Get a small generator; it'll run a furnace blower and you'll be ok in your own house while everyone else is shivering in the dark. :) |
| All times are GMT -4. The time now is 05:50 PM. |