100 Amp Subpanel ?'s - Electrical - DIY Chatroom Home Improvement Forum
Old 03-16-2014, 12:38 AM   #1
Rewards Points: 79
Have 250 amp going into the house. However my main panel is small and I believe is only 200 amp? Will have to check. Either way it's full and I would like to add a 100 amp sub panel.
I want to put it in the basement which is about 40-50 ft away from main panel in the garage. I am looking for an actual diagram and size of wiring to do this. I've done plenty of electrical work but after reading I have become more confused with panels needing breakers some not and the grounding bars.
jbean8510 is offline   Reply With Quote
Old 03-16-2014, 01:02 AM   #2
Banned Electrician
HARRY304E's Avatar
Rewards Points: 198
You don't have 250 amps going into a house.
Look at the panel and see what the largest breaker is.
"Government is not the solution to our problem; Government is the problem."
HARRY304E is offline   Reply With Quote
Old 03-16-2014, 08:01 AM   #3
Licensed electrician
Rewards Points: 3,372
I think you mean 240 volts, not 250 amps.
Have you done a load calculation? I doubt you need 10ⁿ0 amps for the basement.
Old 03-16-2014, 08:14 AM   #4
Civil Engineer
Rewards Points: 2,618
This topic has been discussed many times on this forum, do a search for "add subpanel" or similar you will find dozens of threads. The actual process is pretty simple if you have electrical experience. You add a 100A 2 pole breaker to your existing panel, and run 3 wire with ground cable to the new panel. Two hots, typically red and black, one neutral (white), and a ground wire (typically green). At the new panel, you keep the neutral and the ground separate, which may require you to remove the bonding screw from the panel. Find the threads, this process is discussed at length in some of them, my post is the short version.
You need to discuss cable size with your local wiring inspector. In my jurisdiction, #2 copper with a #6 ground wire is necessary. However, you will find numerous on line discussions that indicate that #4 copper is acceptable, or sometimes #3 is indicated. It seems to be a question of how the local authority interprets the NEC, which is why I suggest discussing this issue first with your wiring inspector. You can also use aluminum wire, however it has to be larger than the copper wire, and you will need to use an aluminum wire rated panel and breaker.
As to whether you need a main breaker in the subpanel, that should also be discussed with your wiring inspector. If the panels are in sight of each other, I believe the inspector may allow for main lugs only on the subpanel, but in my town you always need a main breaker. Sizing the main breaker is a little tricky.
In principle, the upstream feeder wires are protected by the 100A breaker in the main panel. In my town, the subpanel breaker is sized consistently with the main panel breaker, or smaller if the rating of the subpanel is less than 100A in your case. The curious question arises if you purchase a 150A rated subpanel, can you put a 150A rated main breaker in it? Perhaps so, because all the downstream wires are protected by their own breakers, and the upstream wires are protected by the 100A main breaker, so the only thing being protected by the subpanel main breaker is the panel itself. But this is a call for the wiring inspector. Good luck with the project.
Old 03-16-2014, 08:56 AM   #5
A "Handy Husband"
rjniles's Avatar
Rewards Points: 2,790
M comments in bold
This is an unusual requirement and is not part of the NEC. The NEC does not require subpanel to have a main breaker as long as the sub is in the same structure.
Again a unusual requirement not called for in the NEC. a main breaker in a sub panel is merely a disconnect and can be any size; typically the same or larger than the breaker feeding it from the main panel.
Coastal South Carolina
The Following User Says Thank You to rjniles For This Useful Post:
MTN REMODEL LLC (04-13-2014)
Old 03-16-2014, 10:20 AM   #6
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,788
They are interpreting the code wrongly, that is the problem. #4 cu. should only be used on the service conductors at 100 amps. #3 cu. must be used after the main breaker for 100 amps... People use the wrong tables, that's the only issue.
main breakers are only required in sub-panles in detached structures. Another case of the, this is how we're doing it in my town mentality....
The Following User Says Thank You to stickboy1375 For This Useful Post:
Old 03-16-2014, 01:29 PM   #7
Rewards Points: 519
The rule allowing # 4 copper to a 100 amp sub panel is correct , at least in the 2011 code book . Did not have a 2014 code book handy .
It says for residential services and feeders . This would be a feeder .
But as has been stated , it all comes down to what the AHJ says .
God bless
Wyr
WyrTwister is offline   Reply With Quote
Old 03-16-2014, 01:31 PM   #8
E2 Electrician
God bless
Wyr
Sorry, but you are reading it wrong... It has nothing to do with a AHJ, it has to do with being able to read the NEC. To sum it up for you, you can only use #4 if it is going to supply the ENTIRE load, a sub-panel obvious does not meet this requirement.
Old 03-16-2014, 03:03 PM   #9
I am
Agreed....
310.15(B)(7).
service to panel 100 a main breaker cu #4 (seu al 2).............does not apply to sub panels from that panel.
the way I see "feeder" in that article.
service to Main breaker enclosure cu #4 (seu al 2). Main breaker enclosure to remote main panel cu #4 (ser al 2).
UnclePhil is offline   Reply With Quote
Old 03-16-2014, 03:13 PM   #10
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If the service is 100A, you could use #4 to feed a 100A sub panel.
If the service is larger than 100A you have to use #3.
Old 03-16-2014, 03:18 PM   #11
I am
sounds good.
100 amp service. #4 to sub panel. someone upgrades 100 amp service to 200 amp. now what?
Old 03-16-2014, 03:25 PM   #12
k_buz's Avatar
Originally Posted by UnclePhil View Post
sounds good.
You'd have to feed the sub with a 90A breaker.
Old 03-16-2014, 03:29 PM   #13
I am
thank you
Old 03-16-2014, 03:33 PM   #14
k_buz's Avatar
I should clarify...
You could use #4 in the first scenario, if the service used #4. If, for some reason it used #3, you couldn't use the #4.
This is based on the 2008/2011, the 2014 has a new, F-ed way to calculate what needs to be used.
Old 03-16-2014, 04:16 PM   #15
Rewards Points: 326
What's going on in this basement that the OP thinks it needs a 100a subpanel?
IslandGuy is offline   Reply With Quote
Shed subpanel BrandonD Electrical 21 10-14-2012 12:06 PM
Several Questions...leading to Garage Subpanel willstutely Electrical 5 01-03-2012 01:38 PM
Subpanel Right Below Main dcapone Electrical 6 01-02-2012 04:46 PM
Problems with Square D Subpanel bltglt507 Electrical 16 12-04-2009 08:44 PM
A few slightly different questions on subpanel wiring. Chris Dopp Electrical 8 06-26-2009 09:45 PM