An older addition has 2 baseboard heaters wired to 1 thermostat, and I need to extend the wire to move the thermostat to a new location.
The baseboard heaters are probably about 10+ feet long each. Unsure their wattage.
From what I can see on the current wiring, it looks like 10 gauge, it says 10TW 600V on it.I wanted to confirm that I should use 10 gauge wire since I wasn't fully sure if 10TW was 10 gauge, or even thicker (8 or 6).
In the panel this is wired up to a 2 space, 30 amp breaker with a common trip, like this one:http://electrical.hardwarestore.com/...er-605041.aspx
Should I use 10 gauge wire?
RocketManZ is offline   Reply With Quote
Old 12-17-2011, 12:56 AM   #2
Missouri Bound's Avatar
10 TW is 10 guage wire. It precedes the current THHN or THWN wire. It was common 20-30 years ago and was replaced by the current wire designations. You will notice that the insulation is considerably thicker and less "slick". THHN is much easier to pull through conduit, and the newer wire is designated for wet locations (THWN). 10 guage wire is what you should use.
Old 12-17-2011, 12:59 AM   #3
DIY
Rewards Points: 39
Thanks, I was hoping to hear that. You are right this wire looks so darn thick but I was suspecting 10 gauge with an old school coat.
Is 10 Gauge NM-B acceptable?
Sounds like i'll be off to the store to buy 10 gauge wire tomorrow.
Old 12-17-2011, 11:22 AM   #4
DIY
Rewards Points: 39
Can anyone confirm if NM-B is ok in this scenario? Or must I use THHN? This is an inside application.
Old 12-17-2011, 01:19 PM   #5
I=E/R
a7ecorsair's Avatar
10 NM-B will be fine too.
a7ecorsair is offline   Reply With Quote
Can a baseboard heater circuit be 30 AMP? danielrg Electrical 21 04-05-2013 06:51 PM
Electric Baseboard Heat - relay problem? sporkman HVAC 7 11-21-2010 07:43 PM
Crown Boiler closed system baseboard heat chefscott67 HVAC 4 11-04-2010 09:43 PM
Baseboard Heat 80% Rule Question bltglt507 Electrical 1 11-06-2009 12:17 PM
Why do baseboard heaters have 2 circuit breakers? mhaucke Electrical 4 07-08-2007 06:10 PM