10 Gauge Pigtails In Subpanel For 60 Amp Service? - Electrical - Page 4 - DIY Chatroom Home Improvement Forum
Old 04-09-2010, 02:47 PM   #46
I wish I were in that room to look around, I'll bet there's many more violations in the work he did - and I'm sure some of them are unsafe...
Willis
williswires is offline   Reply With Quote
Old 04-10-2010, 09:10 AM   #47
I have gas!
Clutchcargo's Avatar
Rewards Points: 1,374
The electrician monitored usage and come up with 30A/42A/52A on each of the phases at peak demand. He's balancing the loads to be more equal but even he mentioned that he would like to see more amps available.
I've been thinking about the ground jumper bar. If you remove the bar and there is a ground fault. Is the breaker that would trip be where the ground and neutral are bonded? In this case a different inaccessible basement.
I tear things down and build them up.
Clutchcargo is offline   Reply With Quote
Old 04-10-2010, 09:39 AM   #48
Master Electrician
Rewards Points: 3,918
The branch circuit breaker feeding the fault should be the one to trip.
brric is offline   Reply With Quote
Problems with Square D Subpanel bltglt507 Electrical 16 12-04-2009 08:44 PM
Remodel - Moving from 200 amp service to 320 amps stevedar Electrical 20 11-29-2009 08:14 PM
A few slightly different questions on subpanel wiring. Chris Dopp Electrical 8 06-26-2009 09:45 PM
Can I wire a new panel without service or run a "big" subpanel? tigereye Electrical 7 03-03-2009 04:00 PM
Grounding for two service entrances to same house. jogr Electrical 18 09-24-2008 10:31 AM