10/3 To Outside Generator Inlet - Electrical - DIY Chatroom Home Improvement Forum
Old 09-10-2012, 09:31 AM   #1
10/3 to outside Generator Inlet
Hi Folks,
I know it's not best practice to run jacketed NMB cable in conduit. I plan to install a 30A generator inlet about 20 feet from the panel. The location of the inlet is such that I will come out above the sill plate (I have 18" high trusses so lots of room), and down the foundation about 6 feet (it's a walk out style).
Question: Is it acceptable to run the final six or so feet of 10/3 down the outside of the foundation to the inlet box using 3/4" rigid sched 40 conduit? Or do I need to run THHN in conduit all the way to the panel?
I'll staple the rest up inside the trusses once I am inside.
Cheers,
Jeff
aquasport17 is offline   Reply With Quote
Old 09-10-2012, 09:56 AM   #2
Cruising into the sunset
JulieMor's Avatar
Rewards Points: 518
You can run the NMB inside the conduit.
JulieMor is offline   Reply With Quote
Old 09-10-2012, 10:03 AM   #3
Rewards Points: 160
You cannot run NMB inside conduit, outside.
The Following User Says Thank You to J. V. For This Useful Post:
mpoulton (09-10-2012)
Old 09-10-2012, 10:06 AM   #4
So I have conflicting answers.
NEC actually prohibits this? I didn't think that was the case - just thought it was not recommended. Figured with the short distance it wouldn't be an issue.
Would it be considered a "raceway" if the conduit was not terminated at the panel? I'm just trying to protect the wire outside for 6 feet.
Old 09-10-2012, 10:45 AM   #5
Electrical Contractor
jbfan's Avatar
Rewards Points: 490
NMB can not be used in a wet location, and outside is a wet location.
You can use the conduit inside and go through the foundation into the inlet box.
Old 09-10-2012, 10:59 AM   #6
Assuming I am not going to drill through the concrete wall - Is there another method?
Old 09-10-2012, 11:16 AM   #7
I'll just pull four wet location suitable, 10 guage THHN conductors through the conduit to the panel. Any problem with that?
Old 09-10-2012, 11:22 AM   #8
jbfan's Avatar
Rewards Points: 490
Not as long as you use a junction box to transition from the nmb before going into the conduit, and use thwn/thhn, which most wire is dual rated today anyway.
Or you could use uf cable.
The Following User Says Thank You to jbfan For This Useful Post:
aquasport17 (09-10-2012)
Old 09-10-2012, 11:29 AM   #9
Can I just run the UF-B right to the panel with no transition other than from the conduit (once it enters the house)? It's about 20 feet through the trusses. I'll staple it up and away.
Old 09-10-2012, 05:22 PM   #10
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,216
Yes you can.
Coastal South Carolina
10/3 wire to 6-20 receptacle mga56grg Electrical 4 03-27-2012 02:52 PM
conduit for 10/3 interior niche Steve Burke Electrical 4 01-29-2012 11:16 AM
Short ciruit with Romex 10/3 cable and cable connectors virago Electrical 21 10-07-2011 08:01 AM
Splitting 10/3 John J Oswald Electrical 4 05-24-2011 05:16 PM
20 amp breaker on 10/3 wire Duane 70 Electrical 6 09-16-2008 01:02 PM