10/2 Max Amps Rating - Electrical - DIY Chatroom Home Improvement Forum
Old 11-20-2012, 07:19 PM   #1
Rewards Points: 248
10/2 max amps rating
The specs for 10/2 UF romex is 30 AMPS and 600 volts. Do amps ratings always pertain to the voltage rating for a given wire 600V or do they pertain to 120V?
jackwashere is offline   Reply With Quote
Old 11-20-2012, 07:20 PM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Up to 30 Amps, Up to 600 V, you cannot exceed either.
Old 11-20-2012, 07:23 PM   #3
Semi-Pro Electro-Geek
Rewards Points: 2,860
The current rating and voltage rating are unrelated. There is no trade-off between them, if that's what you're asking. The current rating is based on the diameter of the wire and the temperature limits of the insulation. The voltage rating is based on the dielectric strength of the insulation.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
12 AWG wire adequate for 20A 240V (~19A continuous load)? ChootarLaal Electrical 22 07-18-2011 11:58 AM
Generator as sole power source NGuy Electrical 29 12-20-2008 01:29 AM
15 or 20 amp socket with #10? Mdbuilder Electrical 16 12-11-2008 01:27 PM
Max amps allowed - electrician advice needed Des Electrical 27 06-05-2008 11:31 PM
Question about sharing nuetral (as in 12/3) wire Piedmont Electrical 19 01-22-2008 09:39 PM