10/2 Cable - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 08-27-2012, 11:50 PM   #16
" Euro " electrician
frenchelectrican's Avatar
Originally Posted by stickboy1375 View Post
I was hoping you were going to post a pic.
Okay, so this is how you size a unit... you take that MIN circuit ampacity, which happens to be 20.5 amps, now, we look under table 310.16, #12 is good for 25 amps because we are not restricted to 240.4(D) requirements... #14 AWG is good for 20 amps by the way, but your unit is just over this.
Next, the maximum circuit breaker is 30 amps, so that is perfectly fine on # 12 AWG, because the motor contains the over current protection, thus... the circuit breaker is only providing ground fault and short circuit protection.
I do pretty much the same thing as you did size the conductor to the minuim and breaker or fuse at max setting.
But for the rest of reader there is a thorn on this one if not watching this part is if you read the nameplate carefull due one of the poster posted the photo and it stated both Fuse and Breaker the poster can go either way but if say Fuses only then I have no choice but use the fused disconnect switch to meet the codes. ( this one of few spot the inspectors will nail ya if not watching the label )
Merci,
Marc
Old 08-27-2012, 11:58 PM   #17
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Merci,
Marc
As much as I agree, I've yet to come across a unit that only required fuses.... maybe more common in the commercial field?
Old 08-28-2012, 12:04 AM   #18
It used to be real common in commercal side but it seems they are start to use the breaker without issue but I am little lerry on them ( the key issue is AIC rating and how the unit can stand it )
But there were few time I end up installed fused disconnect switch next to the RTU when the specs called for.
Majorty of my time my SOP is call the manufacter to get the cut sheet to verify the info. Sometime the HVAC contractor will inform me mais ( but ).,,, I still want to see it in print to CYA on that part.
The resdentail units that is pretty rare nowdays due most are dual listed but once a while it will show up say fuse only.
Merci,
Marc
Correct cable for 10/2 in NM conduit greg619 Electrical 18 05-10-2012 11:12 AM
Inside Walls Cable Fishing/Routing tk3000 Building & Construction 9 07-05-2011 08:15 AM
Re-route dryer electric cable Stu27 Electrical 10 09-06-2010 08:21 PM
Cable question tommy_vercetti Home Theater 15 09-26-2009 09:10 AM
Coaxial Cable Question bahaisamurai Home Theater 9 08-08-2007 02:54 PM