Old 05-15-2013, 11:43 AM   #31
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
Originally Posted by mm11 View Post
If the raceway is exposed to weather, it's a wet location. I can't think of a raceway I've ever run outside that wasn't exposed to weather for at least some portion of the run.
DAMP or WET ??
artical 100
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline
Old 05-15-2013, 11:48 AM   #32
Rewards Points: 516
Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some cold-storage warehouses.
Location, Dry. A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.
Location, Wet. Installations under ground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
Old 05-15-2013, 11:58 AM   #33
JW
mm11's Avatar
Rewards Points: 592
What's your point Philly?
Exposed to weather= wet location
mm11 is offline
Old 05-15-2013, 01:20 PM   #34
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
So if the outside of the conduit is "exposed to weather" that make the inside a wet location?
Where can I find this in the code book? I am curious.
Speedy Petey is offline
The Following User Says Thank You to Speedy Petey For This Useful Post:
Philly Master (05-15-2013)
Old 05-15-2013, 01:44 PM   #35
JW
mm11's Avatar
Rewards Points: 592
Originally Posted by speedy petey View Post
so if the outside of the conduit is "exposed to weather" that make the inside a wet location?
Where can i find this in the code book? I am curious.
300.9
mm11 is offline
The Following User Says Thank You to mm11 For This Useful Post:
sirsparksalot (05-15-2013)
Old 05-15-2013, 01:48 PM   #36
Rewards Points: 516
Not wet ....unless its buried...
Take a 3R panel. Is it Waterproof ? NO......But u can use it outside all by its self, and only protects from rain etc ..but a
4, 4X is different
http://en.wikipedia.org/wiki/NEMA_enclosure_types
Old 05-15-2013, 01:58 PM   #37
Rewards Points: 506
I can't give the citation, but every time someone asks about NM ran in conduit underground, everyone says the conduit is considered a wet location
Installation is the Reverse of Removal.
sirsparksalot is offline
The Following User Says Thank You to sirsparksalot For This Useful Post:
Old 05-15-2013, 02:03 PM   #38
Rewards Points: 516
I agree and mm11 has right code section...for buried stuff
The Following User Says Thank You to Philly Master For This Useful Post:
Old 05-15-2013, 02:05 PM   #39
Rewards Points: 506
300.9
Yep, and 300.5 (B) covers Underground locations as being wet.
Thanks, mm.
Old 05-15-2013, 02:06 PM   #40
JW
mm11's Avatar
Rewards Points: 592
4, 4X is different
Incorrect- refer to 300.9 and the definition of wet locations you posted earlier.
You're posting about enclosures now, which is a tangent from the current discussion.
For example, the LFMC in this pic is installed in a wet location, and the interior of the raceway is also a wet location.
mm11 is offline
Old 05-15-2013, 02:07 PM   #41
Rewards Points: 506
310.9, yes, above grade wet location
Old 05-15-2013, 02:17 PM   #42
Rewards Points: 516
310.8 ...... .'??? 2008
Old 05-15-2013, 02:32 PM   #43
JW
mm11's Avatar
Rewards Points: 592
Philly, I don't have my 2008 codebook with me. All my sections were from the 2011 edition. There is no 310.8 in 2011, so I'm not sure what you're referencing.
mm11 is offline
Old 05-15-2013, 02:35 PM   #44
Rewards Points: 516
We are 2008 up here in philly area.... Was added in 2008
Old 05-15-2013, 04:13 PM   #45
300.9
Thank you. I had forgotten about that section. I was thinking of 300.5.
Closed Thread
Critique my Panel Wiring Please Ocelaris Electrical 14 03-16-2013 02:10 PM
Extending Wiring Before Circuit Panel... Zeigh Electrical 3 03-02-2013 08:36 PM
AC wiring question? Ralph III Electrical 4 03-04-2012 11:52 AM
AC wiring questions? Ralph III HVAC 0 03-04-2012 11:12 AM
electric wiring in house remodel wis_remod Electrical 6 04-02-2009 03:40 PM