1 Neutral; 2 Circuit Breakers - Electrical - DIY Chatroom Home Improvement Forum
Old 07-24-2011, 11:38 AM   #1
Rewards Points: 121
1 neutral; 2 circuit breakers
I have one 14/3 wire going to one box in my kitchen in which one hot connects to that receptacle. The other hot goes to another box and connects to that receptacle and all share the neutral. Each hot is connected to its own 15 amp circuit breaker. Is this ok or should this just be one circuit and cap the other hot and not use it?
readar is offline   Reply With Quote
Old 07-24-2011, 11:46 AM   #2
Licensed electrician
Rewards Points: 1,622
This is called a multi-wire branch circuit. Properly wired, they are safely used everyday.
The hots should be on opposite legs of the panel to prevent overloading the neutral.
Old 07-24-2011, 12:01 PM   #3
Rewards Points: 121
Thanks. They are on the same side of the panel (CEB from the late 70's) one right under the other, is this correct?
Is it because the hots would be on different phases that makes this safe for the neutral to carry both loads?
Old 07-24-2011, 12:19 PM   #4
Most panels are wired with the buss arrangement ABAB from top to bottom. With the breakers one above the other this puts the hots on opposite legs and the neutral will only carry the difference of the current between the two hots.
If the hots were on the same leg, the neutral could be carrying twice the current as the hots and create a fire hazard.
Old 07-24-2011, 01:00 PM   #5
Rewards Points: 121
Ok, thanks Jim. I'm good then, and I learned a thing or two.
Old 07-24-2011, 01:08 PM   #6
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
To be totally correct the 2 breakers should be tied together (a handle tie) so that both are turned off at the same time. The same can be accomplished with a 2 pole breaker.
Coastal South Carolina
Old 07-24-2011, 01:30 PM   #7
Mad Scientist
If this circuit was installed prior to the 1996(?) NEC, the breakers don't have to be tied together unless both circuits terminate on the same yoke, like with a split receptacle. It's still a good idea, though, and if it were me I'd probably still put a handle tie on the two breakers if they're already right next to each other.
McSteve is offline   Reply With Quote
Old 07-24-2011, 01:50 PM   #8
The Op is in Canada. Although both suggestions are good I am not sure if the CEC has similar requirements as the NEC.
Old 07-24-2011, 01:53 PM   #9
Mad Scientist
Whoops, that'll teach me. Nevermind then, I know next to nothing about the CEC.
Old 07-24-2011, 02:30 PM   #10
Rewards Points: 121
The suggestions sound good and I have a spare double pole breaker so I will swap them out. That way the box will be totally dead when the breaker is turned off.
Old 07-24-2011, 03:23 PM   #11
Electrician
Rewards Points: 794
No breaker tie is neccassary unless there on the same plug. In the box where the 14/3 enters there should be a joint on the neutral and a pigtail to the plug. The neutral of the 14/3 can not be connected right to the plug.
darren is offline   Reply With Quote
Old 07-24-2011, 09:22 PM   #12
I just found this in my house because I saw a wire coming out of an outlet and ran to a pull light but when I turned off the breaker for the outlet the light wouldn't go out then I did some investigating and I saw the red wire I was just about to ask about this
jmans8666 is offline   Reply With Quote
Old 07-24-2011, 09:58 PM   #13
Missouri Bound's Avatar
The breaker tie or double pole breaker is a good idea, regardless if it's required by the NEC. It offers additional safety should you need to work on the circuit or if there is an overload it will de-energize the neutral.
Circuit breakers owlwomyn Electrical 3 06-23-2011 04:00 PM
Tripping breakers,neutrals,120 volts and 240 volts OH My!!! Stubbie Electrical 17 06-11-2011 06:09 AM
Multi Wire Branch Circuit MWBC w/4X or 6X hots or more, 1X oversized neutral mysterylectric Electrical 7 05-05-2011 10:16 PM
Circuit tester shows open neutral; multi-meter says something different. fredgmeyer Electrical 11 10-26-2009 12:41 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 04:58 PM