Thumbs up
york heat pump
my york heat pump is tripping main breaker
in early stage of trouble shooting found small animal was nested in control wire area of condensor
cleared all out and reset breaker
it seems with the thermostat off the condensor is still humming even with the contactor in the open position
what could be the bad component?
mrje5 is offline   Reply With Quote
Old 03-16-2011, 12:43 PM   #2
ok thanks
Old 03-16-2011, 01:25 PM   #3
Still Learning
?? What was the answer?
thehvacguy is offline   Reply With Quote
Old 03-16-2011, 03:03 PM   #4
no answer yet
Old 03-16-2011, 03:20 PM   #5
Still Learning
Does the fan come on too? Or just the compressor?
Old 03-16-2011, 04:14 PM   #6
yes the fan comes on also like at half speed
Old 03-16-2011, 07:57 PM   #7
Still Learning
With the thermostat off do you have 220 volts coming out of the top of the contactor?
Old 03-16-2011, 08:53 PM   #8
AKA HVACTECHFW
Rewards Points: 1,208
check your capacitor
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 03-16-2011, 09:36 PM   #9
Still Learning
Haven't experienced a bad cap yet... How would that cause the compressor to hum?
Old 03-16-2011, 09:49 PM   #10
AKA HVACTECHFW
a weak or bad capacitor will cause a hum from the load (compressor or fan motor) due to not being able to start or trying to start. there is a more technical explanation but I'm not the one to explain that.
More than likely the hum is from the contactor but the fact that the fan motor runs but doesn't seem full speed tells me that most likely it is a dual run cap and the compressor side has failed. Most likely the capacitor has swelled. Would look similar to this.
IT IS WHAT IT IS
Old 03-16-2011, 09:52 PM   #11
An old Tradesmen
Rewards Points: 6,132
If it shorts to ground, you can end up with a completed 120 volt circuit.
Could also be a short in the condenser fan motor, or the compressor.
Old 03-16-2011, 09:56 PM   #12
Still Learning
Thanks for the knowledge guys i really apreciate it. I have seen bad caps on tge way to the trash, but not in troubleshooting. What i dont understand is how that can happen with the contactor not energized?
Old 03-17-2011, 04:41 AM   #13
An old Tradesmen
Single pole contactor has a us that is always hot.
Old 03-19-2011, 02:28 PM   #14
mrje5
ok problem solved thanks to all that helped. here is what happen the animal shorted out the wire harness for the fan at the plug-in connection on the compressor/fan coil side of the harness. after trying all the things suggested i decided to try and splice the wires together eliminating the quick connect.
PROBLEM SOLVED ALL IS WORKING FINE.
Thanks again to all that responded.
New Install - Heat Pump Woes... mark1210 HVAC 7 03-07-2010 10:14 AM
Comparison and Heat Pump Selection help... ChrisDIY HVAC 7 03-06-2010 09:34 PM
New Heat Pump..questions? ddave23 HVAC 4 03-05-2010 06:13 AM
Getting a House..heatpump or no? DavidsCPU HVAC 10 02-07-2010 11:22 PM