York Furnace Ignitor Glowing, But Not Lighting - HVAC - DIY Chatroom Home Improvement Forum
Old 12-28-2012, 12:37 PM   #1
York furnace ignitor glowing, but not lighting
I have a York furnace model P2MPD12N06401B that intermittently will not light, and blows cold air in the house. The sequence of events is:
1. On call for heat, exhaust blower comes on.
2. About 15 sec later, ignitor (at far right burner) glows bright orange.
3. A click can be heard, but burners do not ignite. Very faint gas smell.
4. Ingitor cools down again.
5. Steps 2-4 repeat two more times.
6. Blower motor comes on, exhaust motor goes off, and control board LED flashes 7 times. Cool air blows into house.
I had this problem in March 2012, and replaced control board based on discussion with online parts supplier. It worked fine for the rest of last winter's heating season. Note that unit runs on propane, I have gas, and two other furnaces (not same model) in the same location, fed by same gas line, work fine.
mtdugge is offline   Reply With Quote
Old 12-28-2012, 01:28 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,440
Could be several problems. More than likely the gas valve is sticking and not opening properly and giving enough pressure. Would need to have a Pro with a manometer check the manifold pressure when this happens. Sometimes we have to cycle the unit 2 dozen times B4 it acts up and sticks but 95% of the time it will. Most techs are not patient enough to do that but an experienced one knows better.
Burners may be dirty and gas is not hitting the igniter properly or the igniter is dying and not the exact color of orange it takes to light the gas. The resistance or it and color ( gives U an ignition temp and is important ). I would get the Pro to check the ohms resistance and compare it to a new one.
Igniter may be slightly off center and not exactly in the gas stream but that is VERY rare and only if a inexperienced tech installed it.
Old 12-29-2012, 03:41 PM   #3
Thanks Yuri. I would have replied earlier but did not see your reply until I searched for my message in the postings. I'll get a local pro to check the pressure with a manometer and the ignitor resistance as you suggest.
York Stellar Furnace - help me find my ignitor pmandra HVAC 3 02-17-2012 08:50 AM
RV Furnace Not Lighting rvfoodtruck HVAC 8 11-16-2011 07:19 AM
York G8C Furnace G8CHelp HVAC 43 01-31-2010 10:40 AM
York PM9 Mod Furnace, Aux Fan Question javan HVAC 20 02-10-2009 09:22 AM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 02:55 PM