Wiring a Honeywell RA89A Relay
I am wiring a new Honeywell RA89A relay to turn an oil boiler on and off. The controller for this relay will be a single aquastat on a wood boiler. When the wood boiler is up to temp, it will send power to the relay to shutdown power to the oil boiler burner. Effectively, shutting down the oil boiler when the wood boiler is burning.
The manufacturer of this wood boiler recommended the Honeywell RA89A relay. I am having trouble wiring this relay. It has two TT 24V contacts for a thermostat controller. Because this relay will not be controlled by a thermostat 24V connection, but rather by a 120V line controller from the aquastat, i have jumpered the two TT connections.
I also have the black hot wire coming from the aquastat connected to connection 1 and the white wire from aquastat connected to connection 2. This works, as I can turn the relay on and off (open and closed) using the aquastat temperature dial.
Now for the load (oil boiler burner), I simply snipped the red wire coming from the B1 connetion on the oil burner triple aquastat going to the burner, and ran one end to the relay and the other end to the relay. I was thinking that the relay would then connect and disconnect the power to the oil boiler burner. But where do I connect the load (oil boiler burner) on this relay? From the attached wiring diagram it looks as though I would connect the load to connection 2 and 4. But that would put the line and load on the same connection (2) when I really need these two circuit's to be separated. I have tried using connections 3 and 4 but they have no power regardless of if the relay is opened or closed.
How do I connect the load? Will this relay even work or did they recommend the wrong one?
The first diagram is for the wood boiler and shows how the relay is setup in the wiring scheme. The second diagram is the wiring diagram for the relay RA89A.
Wiring a Honeywell RA89A Relay-woodwiring.jpg   Wiring a Honeywell RA89A Relay-ra89a.jpg
shawnmd is offline   Reply With Quote
Old 10-20-2010, 04:09 PM   #2
An old Tradesmen
Rewards Points: 7,318
The red wire you cut. You should run a wire from it to the #3 terminal of the relay, and then back from the #4 terminal of the relay. This will break the burner circuit.
PS: Remove the jumper from between Terminal 1 and 3.
Old 10-20-2010, 06:05 PM   #3
I have tried tying into three and four with the red wires from the burner, but am not getting any power through those leads. This is what is frustrating me. I have the relay working, but nothing through 3 and 4.
Old 10-21-2010, 12:28 AM   #4
An old Tradesmen
The red burner wire is only energized when the thermostat is calling for heat. Did you have your thermostat set up high enough to call for heat.
Old 10-21-2010, 05:53 AM   #5
Yes, I did have the thermostats turned all the way up. I am actually taking the RA89A back and exchanging it for an RA889 with a NC contact.
Old 10-21-2010, 06:28 PM   #6
An old Tradesmen
But you want a N.O contact.
Old 10-21-2010, 06:52 PM   #7
Actually no, I would want a normally closed so when the wood boiler is not running, and the aquastat is not sending power, the oil burner will run throught the normally closed connection.
Old 10-21-2010, 06:58 PM   #8
An old Tradesmen
We generally use a reverse acting aquastat. Open on temp rise.
Old 10-17-2016, 04:03 PM   #9
Rewards Points: 2
Re: Wiring a Honeywell RA89A Relay
anyone know what L1,L2 hot and to load mean on the above diagram
red68 is offline   Reply With Quote
Old 10-17-2016, 06:52 PM   #10
An old Tradesmen
L1 is the hot wire of the 120 volt, and L2 is the neutral wire of the 120 volt. Load is the circulator.
Honeywell Prestige HD thermostat wiring 1H/1C + Humidification System TekGamer HVAC 0 07-09-2010 11:58 PM
Honeywell Aquastat/switching relay question map83 HVAC 5 12-13-2009 12:21 PM
Heating relay wiring Toledo Electrical 6 11-26-2009 12:03 PM
Wiring a Honeywell ProVision TH8321U1006, upgrade from Weathertron Tstat drandersoninc HVAC 6 10-04-2009 03:20 PM
Trane Heat Pump tstat replacement with Honeywell prog - wiring question sep23 HVAC 2 10-20-2006 09:10 PM