Wiring Aprilaire 700 With Carrier Infinity - HVAC - DIY Chatroom Home Improvement Forum
Old 01-16-2008, 09:43 PM   #1
wiring aprilaire 700 with carrier infinity
I have been doing some reading on the HVAC forums and have not been able to find an answer to my question, so here we go...
I have a Carrier Infinity 58MVP furnace with an Aprilaire 700 humidifier. I just recently installed the Carrier Infinity Thermidistat and am unsure how to wire the humidifier to it. The manual states "a 24vac N.O. Isolation Relay
(DPST) MUST be used to prevent mixing the internal humidifier power with the indoor equipment transformer". Unfortunately, with all of the DIY knowledge I have, I don't know what that swith is, so I am turning to all of you that may be able to lend me a hand. Some of the forums talk about an A50 switch. Is this the same thing and where can I get one? Thanks in advance for any help you may be able to provide.
chburdette is offline   Reply With Quote
Old 01-16-2008, 10:00 PM   #2
Union HVAC Tech.
The power from the thermostat would power the coil on the isolation relay (ie Honeywell R8222D1014) and the relay "NO" contacts would make the humidifier power circuit, or you can use a current sensing relay installed on the heat speed power leg of the blower motor.
bigMikeB is offline   Reply With Quote
Old 01-17-2008, 07:51 AM   #3
I assume that either solution will be straight forward to wire, or is there anything special I should know?
Old 01-17-2008, 11:36 AM   #4
One other note, which is the easiest, prefered, and most commonly used solution. So far it looks like the current sensing relay is easier to install. Thanks again.
Old 01-17-2008, 05:53 PM   #5
Union HVAC Tech.
The current sensing relay is cheapest and the easiest to wire.
Old 01-17-2008, 07:35 PM   #6
Thanks for the reply. I have been doing a little more digging on the current sensing relay and looking at the wiring instructions. This had lead to additional questions. My new t-stat has four wires that go to the board of the furnace. The relay shows that a wire should be connected to the t-stat. The control board on the furnace has a HUM and COM connection. How should this be wired?
Old 01-17-2008, 10:40 PM   #7
Union HVAC Tech.
The "HUM" and "COM" terminals should be used to power a single outlet on the side of the furnace that the humdifier will plug into. The controls on the 700 work best in the auto mode. If you wire the outlet from the board as stated you don't need any other relays, the unit will only be powered when the furnace is running in the heat mode.
Old 01-18-2008, 08:02 AM   #8
Theortically, I think I understand everything, but I do have another question. However, berfore I get to the question, let me give a little more information. Wires come from the breaker panel to a switch on the furnace which shuts power on and off to the furnace if necessary. From that switch, run wires to an outlet that the humidifier is plugged into, I assume to power the humidifier fan. I now have 2-24V brown wires coming from the humidifier that are connected to nothing. What should they connect to?
Old 01-18-2008, 04:11 PM   #9
Union HVAC Tech.
They would hook up to the Aprilaire controller that came with the unit. You should also have an outdoor temp. sensor with that unit.
Old 01-18-2008, 08:35 PM   #10
I think that is where my confusion is coming into play. My T-stat will control the humididty and I don't have to use the control with that came with the humidifier. Here is a link to the instructions for the thermostat I have. http://www.favret.com/pdf_files/ther...on_Startup.pdf
Sorry for the many questions, but I do appreciate the help.
Old 01-19-2008, 07:59 AM   #11
Union HVAC Tech.
The "HUM" and "COM" in your case are only 24v. These terminals will go to the coil on an isolation relay (Honeywell R8222D1014). The two wires from the humidifier will go to the common and normally open terminals on top of the relay. And your done.
Old 01-19-2008, 08:11 AM   #12
Got it. Thanks again. Have a good weekend.
Old 01-09-2013, 07:32 PM   #13
Question
infinity Control on humidifier with isolation relay
The manual "SYSTXCCUID01-B" states on page 5, "24 VAC N.O. Isolation Relay (DPST) must be used ......." but this applies only to the humidifiers with internal power supply. Otherwise I read that humidifiers can be directly connected to "HUM" and "COM/24V" terminals. Question I have is how can you tell if a humidifier has its own internal 24V power supply.
I have a 2 years old Carrier Model 58MVC heater and the same people who installed the heater also installed the Carrie Model HUMCCSFP1016 Humidifier with an isolation relay. After 2 mild winters, both the fan motor and the solenoid on the humidifier went dead. And I put in a new exact replacements but the humidifier is not working due to the dead relay(?)
This humidifier does not seem to have its own internal 24 V power supply. So why the need for an isolation relay? The CPU board in the furnace has "HUM" and "COM/24V" terminals which only get activated (or called for) after the heater kicks in anyway?
So many questions... Maybe I should sign up for Carrier Service Training... only if I can afford it.
Thanks for reading.
Daniel Takayama
dantakayama is offline   Reply With Quote
Old 01-13-2013, 03:06 PM   #14
Carrier to Aprilaire
I'm having a similar problem but mine is a tad more elusive. Your problem however is fairly straightforward and the little that I've figured out I'm glad to offer in the hopes that it'll help. The humidifier unit (eg like a aprilaire 700) itself probably has transfomer power onboard (to power a relay that will turn on the fan) and you can verify this by simply looking on the label affixed to the side of the unit. There will be info disclosing that there is a fan (with power consumption info) and a transformer (24V etc). The two free wires coming from the housing will be merely shorted together (done for you by the connector on the housing when you close it up) and thereby connect power to the relay inside which in turn powers the fan. The relay here in question has nothing to do with the isolation relay that's needed to couple this humidifier to the heating system. The iso relay (a 24V one which you'll supply) would be actuated by the heating system control board (24V via the "HUM" & 'COMMON' connectors) and in turn short the two wires spoken of earlier (via its switch contacts) when the heater blower turns on. Hope this helps.
truite is offline   Reply With Quote
Old 01-13-2013, 04:33 PM   #15
Hi,
Thanks for your input. I did figure out by shorting the blue and red wire that there is not an internal power supply. 120V AC only powers the fan and the humidifier needs the on signal as well as 24VAC from the heater unit. Thus eliminating the need for the isolation relay. I still don't know why the people who installed it originally (2 years ago) put the isolation relay.
Anyway, all is OK now.
Daniel
Carrier Infinity Thermostats / Control4 mistos HVAC 4 12-03-2008 11:02 AM
Carrier Infinity Thermostat "Staging" Adrianjohnm HVAC 2 12-11-2007 01:20 AM
Carrier Infinity T-stat and Performance heat pump gcole HVAC 3 10-03-2007 03:00 PM
Carrier Infinity Control VS Honeywell VisionPRO 8000 Theromostat super_man4471 HVAC 2 04-26-2007 02:27 PM
Aprilaire 700 to Carrier product # FK4BNF003000AAA mag-md HVAC 10 12-17-2006 07:49 PM