Why Does HVAC Shut Off After A Few Seconds - HVAC - DIY Chatroom Home Improvement Forum
Old 09-22-2010, 09:47 AM   #1
I have a Carrier High Efficiency unit that sits in the shade for most of the day. It comes on for about 3 seconds then shuts off for about 10 seconds or so. The furnace fan inside remains on and the house isn't cooling. I sprayed out the outer metal filter of dust but still no change. I don't know the age of the unit, but it was here when I bought the house in 2004.
polomo is offline   Reply With Quote
Old 09-22-2010, 10:16 AM   #2
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
could be several reasons why it is doing what it is but it sounds like the compressor is trying to start and then the built in overload is tripping out. When it resets, it tries again.
It may be something as simple as the capacitor gone bad or it could be something more serious and expensive.
You shouldn't allow it to continue to do this as that can cause additional damage in some cases.
The Following User Says Thank You to nap For This Useful Post:
polomo (09-22-2010)
Old 09-23-2010, 07:40 AM   #3
Is the condenser fan coming on?
Is this how you are determining the 3 seconds on then off.
Does the unit continue trying to start?
If the condenser fan is not starting you may have a bad condenser fan motor.
Artco is offline   Reply With Quote
Old 09-26-2010, 09:08 PM   #4
Yes, the condenser fan comes on. I had it checked out by a tech. The problem was low freon was causing the low pressure switches to trigger the system off. It exists to save the compressor from failure.
thermal equalizer on hvac control question Guam HVAC 4 12-07-2015 03:09 AM
History of HVAC Industry Brands winkydink HVAC 8 03-25-2011 07:28 AM
Shut Off Valve won't shut off DIY_Dumbie Plumbing 1 07-11-2009 02:22 PM
HVAC won't shut off Sling Blade HVAC 7 05-27-2009 12:07 PM
Best 1/2 inch water shut off valve. Nestor_Kelebay Plumbing 10 07-25-2008 11:16 AM