white rogers ignition control


does anybody have any experience with replacing a white rogers 50a55-474 board over to a 50a55-843? this is going to an american standard freedom 90 central air unit all the wiring except a jumper between r01 and r02 on the main plug is the same. Im baffled i can't get the igniter to start up....

Davidj0717 is offline   Reply With Quote
Old 10-16-2009, 07:25 PM   #2
Hvac Pro
 
Join Date: Nov 2008
Location: Winnipeg, Canada
Posts: 9,037
Default

white rogers ignition control


Read the install instructions CAREFULLY and look at it's wiring diagram. There is something about Trane that requires a jumper or removing one for that board I believe. Something to do with the limit circuit or a pressure switch loop.

yuri is offline   Reply With Quote
Old 10-16-2009, 07:47 PM   #3
Newbie
 
Join Date: Oct 2009
Location: illinois
Posts: 14
Default

white rogers ignition control


I did put a jumper on terminals R01 and R02, and i think i followed the correct settings on the DIP switch positions. I have the unit power off right now trying to reset it, and about to turn it back on again.This thing is making be balder by the minute scratching my head!

what exactly are the DIP switch functions? my old board had 3 and my new one has 4....
Davidj0717 is offline   Reply With Quote
Old 10-16-2009, 07:57 PM   #4
Hvac Pro
 
Join Date: Nov 2008
Location: Winnipeg, Canada
Posts: 9,037
Default

white rogers ignition control


Not sure. Do you have the installation instructions? WR is very good at explaining how to setup the board. Did you get the replacement board from Am Std or is it a universal type?
yuri is offline   Reply With Quote
Old 10-16-2009, 08:06 PM   #5
Newbie
 
Join Date: Oct 2009
Location: illinois
Posts: 14
Default

white rogers ignition control


WR, the model board that i had to replace is a 50A55-474 and the wr replace ment is 50A55-843 everything on the board (connections) were the same except for 4 dip switches instead of 3 and the formentioned jumper wire on R01 and R02 that was pointed out on the instructions they said the jumper was needed with trane units but american standard is the same company..
Davidj0717 is offline   Reply With Quote
Old 10-16-2009, 08:11 PM   #6
GC/Master Plumber/Mech
 
Join Date: Feb 2009
Location: Hays, KS
Posts: 1,467
Default

white rogers ignition control


While Trane and American Std are the same company it may not be the same setings.

A Tempstar is an ICP product and so is Carrier but not the same settings or features.

If the instruction says use the jumper for trane it may not be used for a American Standard
__________________
John Wayne once said "Life is tough and it is even tougher if you are stupid"

Tempstar and Trane Dealer
Plumber101 is offline   Reply With Quote
Old 10-16-2009, 08:19 PM   #7
GC/Master Plumber/Mech
 
Join Date: Feb 2009
Location: Hays, KS
Posts: 1,467
Default

white rogers ignition control


On page 3 it says TRANE APPLICATIONS jump RO1 to R02

Says nothing about American Std so don't jump

Set dip sw 1 to ON, dip sw 2 to on, dip sw 3 to off, dip sw 4 to off
__________________
John Wayne once said "Life is tough and it is even tougher if you are stupid"

Tempstar and Trane Dealer
Plumber101 is offline   Reply With Quote
Old 10-16-2009, 09:12 PM   #8
Newbie
 
Join Date: Oct 2009
Location: illinois
Posts: 14
Default

white rogers ignition control


ok dip switch position's are done jumper was removed and im still getting 5 flash's on the self diagnostic display but still no flame and the thermostat is calling for heat.
Davidj0717 is offline   Reply With Quote
Old 10-16-2009, 09:17 PM   #9
GC/Master Plumber/Mech
 
Join Date: Feb 2009
Location: Hays, KS
Posts: 1,467
Default

white rogers ignition control


Flash code 5 is for a flame roll out switch

Need to check the limit that is around the burners, typically these limits are resetable.

Now you need to figure out wy this failed or tripped.

High gas pressure..gas valve failure
Cracked heat exchanger
and so on

I have never and I say again never seen a roll out limit fail. Not to say yours didn't. But there is usually a condition that this limit has caused this flash code.

So, was the board you replaced flashing a 5 code before you replaced it?
__________________
John Wayne once said "Life is tough and it is even tougher if you are stupid"

Tempstar and Trane Dealer
Plumber101 is offline   Reply With Quote
Old 10-16-2009, 09:26 PM   #10
Newbie
 
Join Date: Oct 2009
Location: illinois
Posts: 14
Default

white rogers ignition control


We have two of the same units for the house, i took the board from the working unit over to the disabled unit and plugged it in and get a continuous flash which is good. swapped the board again still a continuous flash. How do i check the limit around the the burner's or and reset them?
Davidj0717 is offline   Reply With Quote
Old 10-16-2009, 09:31 PM   #11
GC/Master Plumber/Mech
 
Join Date: Feb 2009
Location: Hays, KS
Posts: 1,467
Default

white rogers ignition control


When you replaced the board did you make a connection to R01 and R02?
__________________
John Wayne once said "Life is tough and it is even tougher if you are stupid"

Tempstar and Trane Dealer
Plumber101 is offline   Reply With Quote
Old 10-16-2009, 10:39 PM   #12
Newbie
 
Join Date: Oct 2009
Location: illinois
Posts: 14
Default

white rogers ignition control


yes i did put the jumper on at one point.
Davidj0717 is offline   Reply With Quote
Old 10-16-2009, 10:39 PM   #13
Newbie
 
Join Date: Oct 2009
Location: illinois
Posts: 14
Default

white rogers ignition control


but i have since removed it.
Davidj0717 is offline   Reply With Quote
Old 10-16-2009, 10:41 PM   #14
GC/Master Plumber/Mech
 
Join Date: Feb 2009
Location: Hays, KS
Posts: 1,467
Default

white rogers ignition control


If there were no connections between the two terminals when you replace the board then put the jumper between R01 and R02

This should make the flash code stop
__________________
John Wayne once said "Life is tough and it is even tougher if you are stupid"

Tempstar and Trane Dealer
Plumber101 is offline   Reply With Quote
Old 10-16-2009, 10:44 PM   #15
Newbie
 
Join Date: Oct 2009
Location: illinois
Posts: 14
Default

white rogers ignition control


I will go give it a try, the jumper was on but like i said i removed it.

Davidj0717 is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
This may help someone with carrier ignition problems AweMan HVAC 15 02-09-2009 01:20 PM
Off White Trim/Base/Crown with White Ceiling/Doors? StyxTx20 Interior Decorating 4 12-15-2008 07:54 AM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
help with thermostat white rogers cbmm HVAC 1 09-30-2007 04:22 PM
3-way Ceiling Fan Dimmer? 47_47 Electrical 13 09-25-2007 09:31 AM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.