White Rodgers 1F82-261 Tstat To Carrier 38ycc030300 - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 03-12-2013, 05:16 PM   #16
An old Tradesmen
Rewards Points: 6,140
It looks like both yellow and both orange wires are in the same wire nut. If so, they shouldn't be.
Old 03-30-2013, 02:05 AM   #17
Rewards Points: 60
Question
After the yellow and orange wires are separated, the heat worked properly. But when the thermostat is set to AC, the fan in the attic comes on, but the outdoor heat pump does not come on.
Checked the connection from thermostat to Attic to Outdoor units, the connection is:
Thermostat____Attic_______ Outdoor
R -------------------Red-------------Red
G-------------------Orange
O/B----------------------------------Orange
C-------------------------------------Yellow
W2----------------Purple----------White
E jumper to W2
Y no connect
There is black wire from the Attic unit connected to a black wire from the outdoor unit, but not connected to the thermostat. Should these 2 black wires be connected to the C terminal of the thermostat?
And the yellow wire from the outdoor unit connected to the Y terminal of the thermostat instead of C?
chhfsc is offline   Reply With Quote
Old 03-30-2013, 04:39 AM   #18
Houston204's Avatar
Rewards Points: 556
Connect black to thermostat C.
Connect Yellow to thermostat Y.
Blue is not used.
Looks like stat black also needs to be connected to the air handler C.
I only see one black wire there, when I should see two.
Thermostat__________Attic_______ Outdoor
R (red) -------------------R-------------Red
G (green)-----------------G
O/B (orange)------------------------------Orange
C (black)-----------------C----------------black
W2 (white)----------------W1----------White
Y (yellow)-----------------Y------------Yellow
E jumper to W2
Your yellow wires do not connect to the air handler Y.
I would have made this connection, but it probably does not affect anything with this older air handler.
Houston204 is offline   Reply With Quote
The Following User Says Thank You to Houston204 For This Useful Post:
beenthere (03-30-2013)
Old 05-14-2013, 03:16 PM   #19
Rewards Points: 60
A late thank you for all your advice.
Re-wired the thermostat, air handler, heat pump per the last input, it works!!!!
White Rodgers 1F95-1291 Tstat Dual Fuel problem mgroves HVAC 11 02-05-2011 10:00 PM
Need help wiring Honeywell Thermostat from White Rodgers mrx900 HVAC 5 06-06-2010 04:57 PM
White Rodgers 50A50-405 heat blows cold Kbrodsky HVAC 5 05-04-2010 07:19 PM
Making a blower work with a White Rodgers 50A55-405 Controller gegnerx HVAC 3 01-13-2009 04:58 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 10:41 PM