Old 12-05-2009, 08:49 PM   #16
Hvac Pro
yuri's Avatar
Rewards Points: 1,112
There still are a LOT of old Neanderthal boilers (80-100 yrs old) in Wpg. with ugly old millivolt burners etc. Fortunately my plumbers do most of them, LOL.
Old 12-05-2009, 09:52 PM   #17
Problem solved - At least for now.
I checked the transformer at the leads and it was 28v without load. Under load it showed 21v. So all was good with the transformer.
I just crawled back up there and started the furnace cycle. When the voltage was applied to open the valve (a period of 9 seconds), I tapped on the valve case and the combination of the motor trying to open the valve and me tapping on the case let it open up again.
Hopefully it closes! I'll have to check that as soon as it finishes this cycle.
philp is offline   Reply With Quote
Old 12-06-2009, 10:10 AM   #18
Originally Posted by beenthere View Post
Yoz.
Study how solenoid valves/coils work.
My library couldn't get "Fundamentals of Gas Utilitization". I am SOL.
Old 12-06-2009, 10:21 AM   #19
An old Tradesmen
Rewards Points: 6,112
All solenoids work the same(coil wise).
Look how they work on cars, water lines, refrigerant lines. or any thing else.
Old 12-06-2009, 10:27 AM   #20
You know I can't do math!
http://ocw.mit.edu/NR/rdonlyres/4775...0/solenoid.pdf
Valve stuck open and you knew it might = Darwin Award
and
". . .a duty of care is a legal obligation imposed on an individual requiring that they adhere to a standard of reasonable care while performing any acts that could foreseeably harm others."
Old 12-06-2009, 05:24 PM   #21
Originally Posted by Yoyizit View Post
I thought you should get 24.0 vac at the rated VA load with the rated voltage in.
Open circuit voltage might go 10% to 50% higher, because of poor voltage regulation.
What current are you pulling?
A 24v 40 VA 'frmr with 26v open circuit voltage, at 21v, is delivering ~4A.
If Voc = 28v, @ 21v, I = 3A.
YOY are you human? am I questioning a Martian or computer or human or other??
YOU CRACK ME UP!!!!!!!!!!!!!!!!!!!!!!
SULTINI is offline   Reply With Quote
Old 12-06-2009, 05:29 PM   #22
Actually, my existence is defined and indeterminate for those regions outside of Cyberspace. . .
http://www.google.com/search?client=...UTF-8&oe=UTF-8
Here, this should keep you busy for a while
http://en.wikipedia.org/wiki/Artificial_intelligence
http://en.wikipedia.org/wiki/Artificial_stupidity
http://en.wikipedia.org/wiki/Turing_test
BTW, Mr. S., can you find yourself in this list of stock characters?
http://en.wikipedia.org/wiki/Stock_character
Old 12-06-2009, 06:39 PM   #23
Whew I am exhausted and OUT for the night.
Old 12-07-2009, 03:56 PM   #24
24v transformer VA test
If
Voc = 'frmr open circuit voltage
Rload = load resistor value
Vload = voltage across load resistor
then
a = Voc - 24
b = Voc - Vload
and the rated VA
= 24aVload]/bRload
E.g.
Voc = 27vac, Rload = 12 ohms (a common household toaster), Vload = 25 vac
then a = 3, b = 2 and the VA rating is 75.
or
Voc = 28vac, Rload = 12 ohms , Vload = 23 vac
then a = 4, b = 5 and the VA rating is ~37.
This formula may give VA ratings slightly higher than actual.
Old 12-07-2009, 04:26 PM   #25
An old Tradesmen
So what is the starting/opening VA of the solenoid.
Old 12-07-2009, 06:30 PM   #26
That is a State Secret for those of us not in the trade, as you well know but if you have a storage scope and a shunt you could tell me.
Or if you know the coil resistance and coil inductance with the solenoid core in the open position?
This formula is only for the 'frmr.
But,
since a solenoid is a "motor", and most motors want a stiff (i.e., low internal impedance) voltage source, these valves may also want a max. value for the 'frmr's internal impedance, which implies a 'frmr with good voltage regulation.
So a 40VA 'frmr with Voc = 48v may not work, even if the VA are sufficient.
Old 12-07-2009, 09:19 PM   #27
An old Tradesmen
So now do you know why your other post was off base.
Old 12-08-2009, 07:51 AM   #28
Philp
Your statement problem solved - at least for now.
Is a true statement once a valve sticks it will do it again and it will at the time you least expect it 20o outside, holidays, weekends, middle of night.
So the point being replace it ASAP because it will let you down again.
Be prepared.
Old 12-08-2009, 11:33 AM   #29
What #?
Old 12-08-2009, 11:53 AM   #30
An old Tradesmen
Apply the math. And you'll see it doesn't work out like you thing.
How to install Aprilaire transformer? Studly HVAC 9 09-18-2009 10:44 AM
Central Ac transformer question Rschrei518 HVAC 4 10-20-2008 09:21 PM
Low voltage box question WShawn Electrical 7 08-19-2008 07:22 AM
Hard wired Low Voltage Transformer? VistaV Electrical 9 04-25-2008 11:04 AM
Generator Output Question gimmeda8 Electrical 11 03-06-2008 12:15 PM