What Size Main Trunk (extended Plenum)? - HVAC - DIY Chatroom Home Improvement Forum
Old 09-03-2011, 11:47 AM   #1
Question
What size main trunk (extended plenum)?
What size do you guys think I should have for my main trunk that will be 20 feet long? 70,000 btu forced hot air, 2ton ac. 8 inches by ? I keep coming up with 8x20, 8x22, and once in a while 8x18. What do you guys think? Thanks in advance.
Heatless is offline   Reply With Quote
Old 09-03-2011, 06:27 PM   #2
An old Tradesmen
Rewards Points: 6,088
About 8X28
Old 09-03-2011, 11:06 PM   #3
Sizing you main trunk has many things to think about. Is it a straight run? How many heat runs come off of it? what size are they? etc. assuming you have a 70,000 btu furnace your looking at about 12oo CFM which would be 28x8 duct if straight and only feeding 1 floor.
Tin2Win is offline   Reply With Quote
Old 09-04-2011, 05:31 PM   #4
I thought we would figure 400 cfm per ton of ac, 2 ton = 800cfm's that's why I came up with 8x20?
Old 09-04-2011, 07:04 PM   #5
An old Tradesmen
The duct work isn't sized to the A/C because its A/C. Its sized to the one that needs the most air flow. Which in this case is the heat.
Your furnace needs to move more air for heating then it does for cooling. Or you'll end up tripping on the high limit, having very poor heating, and could even burn out the heat exchanger.
The Following User Says Thank You to beenthere For This Useful Post:
Doc Holliday (09-04-2011)
Add Duct to Main Trunk naturalmystic HVAC 3 11-17-2009 03:25 PM
Sub Panel Main Lug Load Center - Single Phase ? Roy Rowlett Electrical 21 08-20-2009 07:55 PM
Furnace plenum size simonb HVAC 1 01-27-2009 10:09 AM
Main Load center Size Evnldr Electrical 11 06-13-2008 11:10 PM
main lug vs main breaker for sub panel diyll Electrical 1 01-17-2008 09:18 PM