Old 07-04-2012, 02:50 PM   #1
Weathermaker 9200 Blower Motor Not Working
Carrier Model 58MXA080-16 blower motor not turning on.
After initiating the Component test sequence by shorting the "test" and "C" terminals, the test starts with the inducer motor running (OK), then the igniter (OK), but the next sequence for the blower motor does not work. I tested the black terminal to common for voltage and no voltage.
Can anyone help with next step of t-shooting.
Steve (Littlefoot)
littlefoot is offline   Reply With Quote
Old 07-04-2012, 03:27 PM   #2
biggles's Avatar
what do you get when you put the stat to FAN/ON no cooling....if nothing remove the stat off the subbase...jump direct R to G that should be diret supply ait fan hi speed....if nothing happen the board in the furnace might be the problem....do the same jump on R to G on the board in the furnace stat still of subbase...
The Following User Says Thank You to biggles For This Useful Post:
littlefoot (07-06-2012)
Old 07-05-2012, 02:11 AM   #3
Jumping R to G seems to energize a relay, but I am not sure what relay it is, and the blower motor does not run. I am back to troubleshooting and will need to check the voltage to the motor.
Update:
Getting there...No voltage present on the output terminals from board when calling for cooling or heating. Applied 120V to the motor lead (black-high speed)directly and fan is running. Turned the thermostat to cool and all systems are functional. Does this mean for certain that the board is bad?
Carrier Weathermaker 9200 error code 31 Espo HVAC 2 03-17-2012 02:45 PM
Carrier Weathermaker 9200 Codes 34/14 have ignition Hawxter HVAC 9 12-31-2011 04:02 PM
weathermaker 9200 not burning tybarr HVAC 1 04-22-2011 09:37 PM
HELP! Carrier Weathermaker Infinity Not Working! MaxPierre HVAC 27 01-19-2009 07:30 PM
RUUD furnace not working blower runs ddeatrick99@hotmail.com HVAC 2 01-16-2008 10:55 PM