#1 |
Water in Furnace exhaust pipe
My high efficiency furnace keeps getting enough water in the pvc exhaust pipe, you can hear it gurgle, to prevent the furnace from working properly. Suck out the water with my shop vac and the furnace runs fine for about a day then I need to repeat the process. How do I fix this?
#2 | |
Sounds like your condensate line is clogged somewhere. Check the tube that comes off the collector that connects up to the condensate drain. If that is clear just keep looking farther down the line.... or if you have a setup that drains to a condensate pump make sure that is working and not backing up.
Live long and prosper. |
#3 |
Check the slope of the exhaust, it must be a minimum of 1/4" per foot to drain properly, sloping back to the unit. Any pooling of water will cause a gurgling sound and the unit to shut-off.
| The Following User Says Thank You to hvac benny For This Useful Post: | ben's plumbing (10-08-2012) |
#4 |
agree with benny check for slope on line ...also check for belly or dip if its a long run....ben sr
#5 | |
Water in Furnace exhaust pipeQuote:
| Display Modes | |
| Installation and support of water heater expansion tanks. | Homerepairguy | Plumbing | 46 | 01-28-2013 06:55 AM |
| Water Pipe Calcs - Interesting Result | ddawg16 | Plumbing | 0 | 05-30-2012 12:19 PM |
| Do I need a ground rod to replace copper water pipe | mfkcbk | Electrical | 10 | 11-11-2010 05:03 PM |
| water borehole question | joeuser | General Discussion | 2 | 04-18-2010 11:33 PM |
| Change in pipe diameter at water heater | blacksheiladog | Plumbing | 2 | 03-06-2009 01:12 PM |