jimsimm 01-04-2011 10:55 AM
I have an International Heater from the 50's in my home that won't turn on this morning. I jumped the thermostat wires at the stat and that didn't work, the pilot is on, the breaker is on, the emergency shut off is on, I can manually turn the fan on, but I can't get the heat on. Any ideas on where to start?
Here's a http://i54.tinypic.com/317ek36.jpg
semore 102 01-04-2011 11:26 AM
Look for a reset button. Usually red. Sounds like a upper limit switch opened. Check filter if it resets
jimsimm 01-04-2011 11:38 AM
I don't see any reset button. I'm looking for my multimeter so I can check the voltage at the valve. If the pilot is lit, as it is, do I need to check the thermocoupler or would that not be an issue since the pilot is lit?
semore 102 01-04-2011 11:52 AM
In your picture. The white button/ switch. Is that a reset. Look up into the hood , see if reset is there. Gas valve should be getting the 24 volts. Open circuit somewhere.
jimsimm 01-04-2011 12:15 PM
thanks semore, that white button is the manual switch for the fan. the fan works when I turn that. I checked the gas valve and it is not getting any voltage. Where do I go from there?
semore 102 01-04-2011 12:24 PM
Do you see the wiring diagram. Look for a upper limit switch. You looked in the hood? Follow the wires from the gas valve, look for any resets.
SKIP4661 01-04-2011 01:14 PM
Looks like an in-line fuse coming off from the transformer on the red wire. If it is a fuse, check to see if it is burned. When you find your meter check the transformer for 24 volts.:)
jimsimm 01-04-2011 01:33 PM
Thanks for everyone's reply. I re-tested everything, and it turns out the Thermostat IS faulty. I don't know why it didn't turn on the first time I tried jumping it, but it did now. Off to the store to get a new one. Thanks again for your help.
hvaclover 01-04-2011 03:47 PM
That is an oil converted to gas furnace. I t has no resettable limits.
hvaclover 01-04-2011 03:50 PM
The white button is for continuous fan and is part of the fan limit control.
hvaclover 01-04-2011 03:53 PM
Not a fuse. Just an insulated fork terminal.