-   -   unit runs fails to clcle off when temperture reaches below 35 degrees (http://www.diychatroom.com/f17/unit-runs-fails-clcle-off-when-temperture-reaches-below-35-degrees-32308/)
luvjww 11-20-2008 11:48 PM
i have a york heat pump unit and it seems to run constantly when temperture is below 35 degrees. i set the inside thermostat to 71 and and i placed a thermometer in the the main pipe to gauge the tempertue in the indoor unit and i noticed that the unit seems to make a straining noise and i read the gauge and it was reading between 100-120f and i use a infarred red thermometer to check the temperture from the vents and they range from about 75-80f. i understad that the temperture coming from the vents would seem to feel cool but i just feel that there is a big difference from the two readings. i anyone have any answers i am open to evey option.
beenthere 11-21-2008 05:31 AM
Is your duct in the attic, or basement.
Is it maintaining temp, but not shutting off.
Ot isn't it maintaining temp at 35 either.
luvjww 11-21-2008 09:26 AM
the duct is in the attic. one thing i noticed is after the aux heat brings the thermostat to room temperture the aux kicks off but the unit continues to run. i am sure it is keeping temperture.
beenthere 11-21-2008 10:02 AM
If you have a didital thermostat, that uses CPH.
Set the second stage CPH to a number lower then first stage, and it will satisfy the heat call in second stage, when it gets to temps below 35..
luvjww 11-21-2008 10:11 AM
im not sure what cph is but my thernostat displays inside temperture and set to and it also displays that the heat is on and when the aux kicks in it also displays
luvjww 11-21-2008 10:16 AM
im not sure what cph is but my thermostat displays inside temp and set to temp and when aux kicks in it also displays
beenthere 11-21-2008 10:36 AM
CPH stands for Cycles Per Hour.
Its one method that some stats use to control the on and off cycle times, and temp control.
Other ones use only temp difference.
Check your install manual, and see which method yours uses.
What brand and model is it.
luvjww 11-21-2008 10:44 AM
it is a honeywell rth3100c non -programmable
beenthere 11-21-2008 01:28 PM
On that stat, I believe its function number 8, to set the aux heat cycle rate lower.
luvjww 11-21-2008 02:35 PM
Ok I will look into trying that.
pbservano 11-21-2008 05:47 PM
This 100-120F temp is the surface temperature at the inlet piping of the indoor unit? If this is so, the vent outlet temp is about the correct temperature(75-80F). If the outdoor temp is below 35F your heat pump efficiency decreases that is why your indoor unit has an auxilliary electric heater to help maintain the temperature at your supply vents. You are still going to experience temperature fluctuation, it is normal. Constant running of your compressor @ 35F is normal. Now, if the your indoor room temperarure is achieve and the compressor (outdoor unit) is still running for a long period of time then you have a problem.Check your outdoor unit for ice accumulation on the condensing coil. If it does happen, then you might have issues with defrost sensor or defrost control board.