Txv - HVAC - DIY Chatroom Home Improvement Forum
Old 09-16-2011, 05:34 PM   #1
Txv
I have a Ruud UPLB-048Jaz and it has a txv at the indoor coil and a fixed orifice at the outside condenser. If I wanted to install a txv on the outside condenser what txv would I need to order? Would I need a kit or would an AC tech have what is needed for the conversion.
carlb7 is offline   Reply With Quote
Old 09-16-2011, 06:01 PM   #2
I'm Your Huckleberry
Rewards Points: 2,270
Huh? What makes you think it has a fixed orifice metering device at the condenser? Is this a heat pump system?
Doc Holliday is offline   Reply With Quote
Old 09-16-2011, 06:34 PM   #3
Rewards Points: 1,214
What makes you think it's the TXV??
COLDIRON is offline   Reply With Quote
Old 09-16-2011, 06:42 PM   #4
JJboy's Avatar
Trying to do reverse engenner
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 09-16-2011, 07:19 PM   #5
An old Tradesmen
Rewards Points: 6,072
Don't what TXV for it. but remember, no guaranty that a TXV improves your heating efficiency.
Old 09-16-2011, 09:25 PM   #6
Don't want to cause too much excitement here! Yes it is a heat pump and yes it has a fixed orifice. Just wanted to know if a 4 ton txv is all that is needed for a conversion. Any other information needed before ordering one?
Old 09-16-2011, 09:35 PM   #7
JJboy's Avatar
No, just the tonnage and refrigerant used
Old 09-17-2011, 02:01 AM   #8
An old Tradesmen
The super heat for the outdoor TXV is often lower then that of the indoor TXV. Installing a standard TXV can cause poor heating performance.
Old 09-17-2011, 07:41 AM   #9
Probably should stick to OEM Parts and equipment. Sounds like you're' heading for trouble. Just saying.
Old 09-17-2011, 10:04 AM   #10
Don't break what's not fixed..or something like that.
You would have to buy a distributor nozzle, with the proper orifice, and the txv. The nozzle will have to be designed for reverse flow, so its going to have to come from ruud/rheem dealer. And its not cheap. By the time you get finished buying parts and having them installed, you will not have improved anything, and be a little poorer for doing it.
Master of Cold is offline   Reply With Quote
Old 09-17-2011, 11:12 AM   #11
All summer long the AC worked perfectly. In the heating season the problem shows up when the unit first comes on, air temperature from the upflow will start at a temperature then drop about 7 to 10 degrees in the first 30 seconds. Then it slowly starts climbing back up. I have checked other systems and this does not occur. I was thinking if it is related to refrigerant flow and that a txv may solve the issue.
Old 09-17-2011, 11:16 AM   #12
Before you can fix the problem you have to find out what is causing it. It could be a sequencer kicking out early.
Old 09-17-2011, 11:16 AM   #13
An old Tradesmen
Its not because of the piston. And a TXV won't cure it. Good chance its a charge related problem.
Old 09-17-2011, 12:36 PM   #14
If the temp dropped 30 seconds after starting then the heat sequencer turned off prematurely. The heat pump wont generate much of a temp rise for at least 30-45 seconds after start-up. Or the thermostat disengaged W1 early.
Old 09-17-2011, 02:18 PM   #15
So let me make sense of this. When the system first comes on and the air temp from the upflow is 95 degrees right at the start, its this temperature because of the heat sequencer? Wouldn't it take time for this heat to build up as well? Then after the system is running for 30 seconds the temperature slowly drops to 87 degrees until it stabilizes before it gradually rises back to the 95 degree temperature( over about 3 minutes or so), levels out and then increases each degree slowly upward until it reaches its maximum depending on the outside temperature.