Two Thermostats In One Heat Zone. OK? - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 12-01-2008, 08:27 PM   #16
Rewards Points: 16
@beenthere
It's a 105K BTU Utica NG boiler.
What are you looking for on the temp rise? It looks to be running about 180F before it cycles off. (It will run constant for about 30-40 minutes when calling for heat, not short cycling.)
fishmanflats is offline   Reply With Quote
Old 12-01-2008, 08:34 PM   #17
Rewards Points: 16
@bulebob
Originally Posted by buletbob View Post
Here is a suggestion!! You could be able to separate the two floors to make two zones from the basement below. that would be the best bet! with a monoflow system, there's usually is a 1" loop with two tee's cut into it. then 1/2" coming from the tee to the rad.. find the monoflow tee that brings the hot water to the second floor and remove it and install a standard coupling on the feed side and the same for the return side. then run a new loop for your zone to the four pipes leading upstairs.don't forget to install the monoflow tee's.
And also check and see if the system was repaired at some point. I have seen Mono flow tee's installed backwards which will make the system not work properly. there should be and arrow on the tee to show the direction of the water flow. BOB.
I looked into doing this last summer. Both plumbers that i had come out never called back. I was guessing about $2500-3000 for the job. The loop is 1 1/2" copper and I'd need about 110 feet (about $1000 for the pipping alone). My basement is partially finished, so I'd need to have some ceiling removed. I figured 30 ft of wire and a new thermostat would be less than $50 and a little easier to get done.
Old 12-02-2008, 12:23 AM   #18
An old Tradesmen
Rewards Points: 6,476
Temp rise, is the difference between return water temp, and discharge water temp.
What is it on your system.
Old 12-02-2008, 06:37 AM   #19
BUILDER / REMODELING CONT
buletbob's Avatar
if I remember correctly that there is just two rads on the second floor, which i would guess you should be able to use 3/4". and you could switch from copper to pex. just another thought. BOB
Old 12-03-2008, 10:07 PM   #20
Rewards Points: 16
inlet outlet temp
I don't have a way of measuring this. The boiler is too old to have these controls. There's only the analog reading on the side.
-Mike
Old 12-03-2008, 10:08 PM   #21
Rewards Points: 16
radiators
I actually have four radiators on the second floor, three in bedrooms and on in a bathroom.
Old 12-03-2008, 10:14 PM   #22
buletbob's Avatar
then the bigger pipe will be needed.
Propane 2 zone heat theleos7 HVAC 6 01-09-2008 06:41 PM
Zone system not working with heat. deliriousga HVAC 5 12-29-2006 07:04 PM