Twinning Issue - HVAC - DIY Chatroom Home Improvement Forum
Old 07-26-2014, 03:57 PM   #1
Rewards Points: 225
Twinning Issue
Here we go...I went out to look at a unit another Tech. was having a problem with. It is a twinned system with York airhandlers/furnaces. The unit cools fine. The problem is that the slave air handler is giving 9 red flashes indicating reverse polarity or missing ground. The blower of the slave will cycle on every hour for about 90 secs. When wiring each system independently they both function with out error codes. The tech. Who worked on it originally replaced the control board on the slave. Ever since then he has had this issue. All the wiring is correct but still can get rid of error code. Any thoughts?
a.man1302 is offline   Reply With Quote
Old 07-26-2014, 05:31 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 2,296
On the board the 24 volt wires from the secondary side of the transformer must be in the EXACT Sec 1 and Sec 2 positions or whatever York calls them. I hade them get mixed up on a York and it gives you a reverse polarity code. Carefully read the markings on the board and wiring diagram to make sure he did not switch them up.
Old 07-26-2014, 05:56 PM   #3
Rewards Points: 225
on the slave air handler he is not using the 24v from the transformer because he is getting his 24v from the master airhandler. He said that was the way it was wired originally
Old 07-26-2014, 06:55 PM   #4
Hvac Pro
yuri's Avatar
The slave air handler still has it's own circuit board and 24 volt transformer. It just gets a signal from the primary one instead of it's own tstat. Has to have a board and transformer to operate.
Old 07-26-2014, 09:52 PM   #5
An old Tradesmen
Rewards Points: 7,402
Usually, the second furnace still has its own transformer. Its just there is a wire added to go from each twin terminal.
Old 07-26-2014, 10:15 PM   #6
Hvac Pro
yuri's Avatar
If your tech/ co-worker was guessing or doing the parts changer routine and did not hook up the wires from the transformer to the new board properly then that may be the issue. I would check his wiring first.
Old 07-27-2014, 03:32 AM   #7
Houston204's Avatar
Rewards Points: 556
Was this twinned setup operating correctly initially?
You may need to move one furnace breaker one space down.
Both furnaces must be on the same bus bar.
Houston204 is offline   Reply With Quote
Old 07-27-2014, 11:15 AM   #8
Rewards Points: 225
According to him, when he changed out the original board that is the way it was wired. He is saying that the he doesn't need the 24v from the transformer for the slave because he's only using one T-stat and he's getting his 24v from the master. He thinks that he's going to burn the board because he would be getting 2 doses of 24v.
Old 07-27-2014, 11:18 AM   #9
Rewards Points: 225
HE also said the twin terminal was not being used with the original board.
Old 07-27-2014, 11:26 AM   #10
Rewards Points: 225
The wiring looks fine except for the fact that he has no low voltage wires connected from the transformer to the board on the slave unit, and he's not using the twin terminals... Like I said according to him that is the way it was wired up when he replaced the board.
Old 07-27-2014, 12:19 PM   #11
Hvac Pro
yuri's Avatar
Sounds all wrong to me. Transformers are rated in VA which means voltamps which is horsepower for the layman. The slave unit has relays which require amps to work and you do not have extra amps to spare with the transformer in the primary unit. Where is it supposed to get the extra power to handle another board and load?
He/you should use the twinning terminal. How the heck it ever worked is beyond imagination and both boards could be damaged from working with one overloaded transformer. When it is overloaded the voltage drops and that kills boards.
Twinning just means a communication signal/handshake goes to the slave and tells it what to do. Contact York tech support and see what they have to say or get him to do it.
Old 07-27-2014, 05:16 PM   #12
An old Tradesmen
Bad twinning set up.
Disconnect the wires from the other furnace. Connect the transformer, and see if you get the same error.
Old 07-28-2014, 09:01 PM   #13
Rewards Points: 225
Well I told him to forget how it was previously wired and sent him a link to help him out.
York Central Tech Talk http://yorkcentraltechtalk.wordpress.com/?s=twinning
Hopefully it will help him out.
Old 07-28-2014, 10:55 PM   #14
Hvac Pro
yuri's Avatar
I see ALL kinds of crap that got done over the years and how it runs is beyond comprehension. Sometimes it is best to rip the wiring out and start back the way it was from the factory and what they recommend rather than waste time figuring out how the wrong setup worked.
Old 07-29-2014, 10:41 PM   #15
Rewards Points: 225
Agreed... Thanks for all your responses... I am waiting to hear back from the tech. who was working on it.