I am trying to get my 12 gallon Honeywell TrueSteam humidifier working here at my house. I have a TrueIAQ controller for the humidifier and a Honeywell RTH7500D for my thermostat. The wirings are:
IAQ to Truesteam : Hum to Hum (2), R and C (24V).
Thermostat to TrueSteam : G to GT
Truesteam to HVAC : GF to G
Thermostat to HVAC : R, W, Y and R and RC is jumpered in the thermostat.
I am unable to run the humidifier via using Fan or heat control. The only way I get it go is by setting it independent of the above two. (ISU setting on 25 to 3 on TrueIAQ). I can get the humidifer to turn on when I set ISU 25 to 2 , but the fan does not kick on).
What am I missing?. I would like the humidifier to turn on only when there is heat.
abasak is offline   Reply With Quote
Old 01-03-2010, 11:40 AM   #2
An old Tradesmen
Rewards Points: 7,414
make sure no wire insulation is under the screw terminals.
Do you have a wire running from the stats W to the IAQ's W.
Old 01-03-2010, 12:20 PM   #3
Looked at all the wiring again and they look fine. All wiring do not have insulation in the screw terminals.
Connected the W between the thermostat and IAQ. Then ran the IAQ with setting 0 on 25 and the humidifier does not kick on. Then I tried 1 and 2 for 25 on the IAQ. Nothing happens in 1 but in 2 the humidifier did kick in ( heating was previously running ). After a while when the heat reached the target and the fan also stopped a while later. But the humidifier kept on working. I do not want this situation where I do not have any sort of air circulation and the humidifier keeps on chugging.
Any ideas.....?
Old 01-03-2010, 12:27 PM   #4
An old Tradesmen
Where is the R and C of the IAQ hooked at on the furnace/air handler?
Old 01-03-2010, 12:30 PM   #5
An old Tradesmen
Is the factory jumper from R to RT missing.
Old 01-03-2010, 12:56 PM   #6
  • Jumper R to RT on the truesteam is present.
  • R & C of IAQ is connected to the 24V on the TrueSteam. That is what the drawings say. ( Page 20, option 2 on the Installation guide) .There is no connection of R & C of IAQ to the HVAC directly.
  • The R & C on the TrueSteam is connected to the R & C on the HVAC
Old 01-03-2010, 01:30 PM   #7
An old Tradesmen
Ooops. meant the R and C of the Truesteam.
And you are not using a pressure switch in the common wire to the HVAC and Truesteam?
Did you check to make sure its sensing voltage from the air handler/furnace.
What brand and model number is your HVAC unit.
Old 01-03-2010, 02:03 PM   #8
  • I do not have a pressure switch installed and C from HVAC is connected to C on Truesteam.
  • HVAC is Rheem RGDJ-12EARJ
  • As far as sensing goes what pins do I check on the Truesteam for the same?. 24V to the IAQ is there......
Old 01-03-2010, 03:01 PM   #9
An old Tradesmen
If you want it to run with the heat. Then on the IAQ, the W should read 24 volts when checked to C of the IAQ during a heat call.
If you want it to run when the fan is turned on by the thermostat. Then the IAQ G to C should read 34 volts when the stat runs the fan.
Old 01-04-2010, 10:36 PM   #10
How do you check W and G on IAQ?. They run from the stat to the IAQ. In order for me to reach the pins, I have to remove the IAQ controller. When I remove the controller all of them loose power !!.
Old 01-05-2010, 04:38 AM   #11
An old Tradesmen
Check to see if the terminals on the Truesteam are receiving voltage.
I miss typed it in the other post.
Old 01-05-2010, 05:32 PM   #12
Beenthere, thanks a lot for your help.
I contacted Honeywell support and they helped me figure out the root cause.......
  • I was not hooked up to a dedicated 12A circuit. I had it hooked up to a 15A circuit that was shared by the furnace and the true steam. Although I was able to make it work partially in this mode and it never occurred to me that I needed a dedicated line as the circuit breaker never tripped. Once I had a dedicated circuit, everything works as per the wiring that I mentioned in the initial post. The fan turns on whenever I need humidity.
  • In order to make it turn on using the furnace/heat the support guy suggested that I need to hook up the R&C from the IAQ directly to the furnace and have W connected between the stat ...have to try that out.
Old 01-16-2012, 06:01 PM   #13
Trusteam air handler fan issue
Stumbled onto this thread, which happens to be the exact same issue I am struggling with. Really appreciate the comments and instructions from the contributors here. Per the final post, I ran the unit directly into a 15A outlet, with no success here. It is amazing that the unit will only "partially run" if you don't have a dedicated circuit.
One question came up when I was rereading the manuals: The IAQ manual states that "pin R - 24V supply "must be common to G output"", what does that mean ? I just attached two wires from the two IAQ power inputs (R and C) to the two Trusteam 24V terminals. Is there more to it ?
Thanks for any help.
Cliffschum is offline   Reply With Quote
Honeywell TrueSTEAM Installation OldCountry HVAC 26 12-13-2009 06:26 PM
Honeywell TrueSteam with Carrier Infinity Control Llama HVAC 1 02-19-2009 04:20 PM
Konecto Installation Tidbit jennydavis Flooring 9 01-06-2009 12:19 AM
Honeywell TrueSteam Humidifier? kcrossley2 HVAC 3 12-01-2008 03:22 PM
Aluminum Soffit and Fascia Installation... MoparAutoworks Building & Construction 1 12-17-2006 07:46 AM