Troubleshooting A Goodman Integrated Control Mod - HVAC - DIY Chatroom Home Improvement Forum
Old 05-29-2010, 10:51 AM   #1
Wink
Troubleshooting a Goodman Integrated Control Mod
The fuse on integrated control module in a goodman model GMT blows almost immediately when replaced in the AC mode. I have check the 120/24 transformer with an ohm meter and it reads no short to ground on either side and the opposite poles are isolated. The board shows no "burned" components or spots from the front. Are there another tests that I might do before replacing this module?
sportster is offline   Reply With Quote
Old 05-29-2010, 11:00 AM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 2,230
The thermostat wiring to the outside unit may be damaged by weed whacker/dog/rodents. Check it first. Then remove it at the unit outside and try turn unit on. If it still shorts then the short is in the wiring to the house or the furnace and not the outdoor unit. Look for dead mice, bad contactor in outdoor unit.
Old 05-29-2010, 11:04 AM   #3
Houston204's Avatar
Rewards Points: 556
Check the control wire to your outdoor unit. Animals and weed eaters commonly damage it.
The control wire can also rub against copper pipes in the outdoor unit and cause this problem.
Houston204 is offline   Reply With Quote
Old 05-29-2010, 12:49 PM   #4
Thank you for your quick feedback. I did what you suggested and I also disconnected the ac unit contact solenoid from the control mod and tested to see if the fan would come on and it did. Then reconnected the outside solenoid and it blew the fuse again. The contact solenoid does show discoloration by not that bad and it read out ok, but I do not have a megger.
Old 05-29-2010, 01:04 PM   #5
Hvac Pro
yuri's Avatar
You don't need a megger just a new contactor from Graingers (under $50). They are rated in amperage draw for the contacts but I would get a 30 amp one as it is the largest and has better contacts. It is probably mechanically seizing and drawing too many amps not necessarily shorting.
The Following User Says Thank You to yuri For This Useful Post:
sportster (05-29-2010)
Tags
control , gmt , goodman , model , module
Goodman furnace control board patz83 HVAC 7 03-14-2010 02:07 PM
Goodman 4 flashes on control board bigmac71201 HVAC 6 09-28-2009 02:53 PM
DIY recommendation for Goodman Control Module (Circuit Board) njwaves HVAC 3 09-26-2009 07:29 AM
S9301A1001 Integrated Boiler Control Invisible-Man HVAC 3 03-31-2009 09:49 PM
Sub is swapping Amana for Goodman Dragon HVAC 22 02-04-2007 07:54 AM